Chapter 2 - Planning
Shipping temperature
Storage temperature
Maximum wet bulb
temperature
Operating humidity
Storage humidity
Airborne Contaminants
Copper Reactivity Level
H2S Gas concentration
S02, S03 Gas concentration
CI2 Gas concentration
NOX Gas concentration
HF Gas concentration
temperature gradation of 10° per hour . Note : for
Altitudes above 2950 feet , the maximum operating
temperature is derated 1 °F/550 ft.
All temperature ratings shown are for sea level. An
altitude derating of 1 °C per 300 m (1.8 °F per 1,000 ft)
to 3048 m (10,000 ft) is applicable. No direct sunlight
allowed.
Runs within the temperature Class/Severity A2 limits
(18-27 ° C) per ANSI/ISA-S71.01-1985 Standard*
-30 °C to 50 °C (-22 °F to 122 °F)
-30 °C to 60 °C (-22 °F to 140 °F)
28 °C (82.4 °F)
ATTENTION
All temperature ratings described previously
are for sea level. An altitude derating of 1 °C
per 300 m (1.8 °F per 1,000 ft) to 3048 m
(10,000 ft) is applicable. Direct sunlight is not
allowed.
20% to 80% (non-condensing) with a maximum
humidity gradation of 10% per hour
5% to 95% (non-condensing) ) with a maximum
humidity gradation of 10% per hour
ATTENTION
Storing maximum humidity of 95% is based on
a maximum temperature of 45 °C (113 °F).
Altitude maximum for storage corresponds to
a pressure minimum of 70 KPa.
Airborne Contaminants < 300 angstroms/month
Copper Reactivity Level < 3 mm3/m3 parts per billion
H2S Gas concentration < 10 mm3/m3 parts per billion
S02, S03 Gas concentration < 1 mm3/m3 parts per
billion
CI2 Gas concentration < 50 mm3/m3 parts per billion
NOX Gas concentration < 1 mm3/m3 parts per billion
HF Gas concentration < 500 mm3/m3 parts per billion
- 23 -