Electromagnetic Immunity And Emissions - Allen-Bradley AADvance T9110 Safety Manual

Table of Contents

Advertisement

Attribute
Shock
Altitude
Operating
Storage and Transport
Electromagnetic Interference
Hazardous Location Capability
IMPORTANT
• This equipment is not certified for use in a Zone 1 location
• This equipment is not certified for use in a Zone 0 hazardous
environment.
NOTE Casing: Standard AADvance modules also have a plastic casing and are
rated IP20: Protected against solid objects over 12mm (1/2in.) for example
"fingers". There is no specific protection against liquids.

Electromagnetic Immunity and Emissions

The AADvance system has been designed and tested to withstand normal
levels of conducted and radiated electromagnetic interference and electrostatic
discharge. Electrical noise conditions may vary greatly, depending on the
equipment installation, wiring, other installed equipment, and its proximity to
the AADvance equipment.
A detailed analysis of the installation electrical and magnetic conditions is rare.
It is therefore necessary to ensure that the system as a whole complies with the
client's requirements or appropriate standards EN 61000-6-2:2005 and EN
61000-6-4:2007; within Europe, the CE mark requirements form a legal
minimum.
For systems for applications outside Europe it is recommended that at least the
same measures be applied, and confirmation sought from the client or end user
that electromagnetic interference (EMI) levels are within those shown in the
table.
Table 17 - Immunity to Electromagnetic Emissions
Standard
Conditions
Radiated Emissions
CISPR11:2003
Class A
BS EN 61000-6-4:2007
N/A
+ A1:2011
Radiated Field Immunity
Rockwell Automation Publication ICSTT-RM446N-EN-P - April 2018
AADvance Functional Safety System Implementation
Value
15g peak, 11ms duration, ½ sine
0 to 2000m (0 to 6,600 ft.)
0 to 3000m (0 to 10,000 ft.)
This equipment must not be transported in unpressurized
aircraft flown above 10,000 ft.
Tested to the following standards: EN 61326-1:2006, Class A; EN
61326-3-1:2008, EN 54-4: 1997, A1; EN 61131-2:2007; EN
62061:2005.
Suitable for Class I Div 2 and Zone 2.
Notes
Not applicable
Access to controller must be restricted to
appropriately trained maintenance
personnel operating in accordance with
and relevant ESD mitigating procedures.
Chapter 4
105