Fairchild T7800 Installation, Operation And Maintanance Manual

Miniature electro-pneumatic transducer

Advertisement

Quick Links

FAIRCHILD T7800 STANDARD RANGE
MINIATURE ELECTRO-PNEUMATIC TRANSDUCER
Installation, Operation and Maintenance Instructions
Figure 1. Model T7800 Standard Range Transducer Identification Number System
GENERAL INFORMATION
The Model T7800 Series of Electro-Pneumatic Trans­
ducer converts a DC input signal to a linearly proportional
pneumatic output pressure.
SPECIFICATIONS
Functional Specifications
psig
[BAR]
(kPa)
3-15
Output
[0.2-1.0]
Range
(20-100)
Input
4-20 mA DC, 0-10 VDC,
Range
1-9 VDC, 0-5 VDC, 1-5 VDC
20-120
Supply
[1.5-8.0]
Pressure
(150-800)
5
Minimum
[0.35]
Span
(35)
psig
psig
[BAR]
[BAR]
(kPa)
(kPa)
3-27
6-30
[0.2-1.8]
[0.4-2.0]
(20-180)
(40-200)
35-120
32-120
[2.2-8.0]
[2.4-8.0]
(240-800)
(220-800)
10
10
[0.7]
[0.7]
(70)
(70)
Identification Number
Electrical Connections
1/2 NPT Conduit
Fitting with Pigtail
Terminal Block
DIN 43650 Connection
Rack Mount
Underwriting Group
Factory Mutual
Canadian Standard
ATEX
Approval Class
1
Intrinsically Safe
Non-Incendive (Division 2)
Input
4-20mA
1-5 VDC
0-5 VDC
1-9 VDC
0-10 VDC
Output
Select appropriate psig, [BAR] or (kPa).
3-15 psig
3-27 psig
6-30 psig
[0.2-1.0 BAR]
[0.2-1.8 BAR]
[0.4-2.0 BAR]
(20-100 kPa)
(20-180 kPa)
(40-200 kPa)
1
Intrinsically Safe approval, including non-incendive
(Division 2), on 4-20 mA units only.
2
Non-incendive (Division 2) approval on FM voltage
input units only.
3 psig
A i r C o n ­
[0.2 BAR]
sumption
(20 kPa)
All Ranges
3.5
3
(SCFH)
(.10 m /HR)
2.5 (4.25m /HR) @
Flow Rate
25 psig, [1.7 BAR],
( S C F M )
(170 kPa) supply &
9 psig, [0.6 BAR],
(60 kPa) output.
Temperature
Operating . . . . . . . . . . . . . . . . . . . . .
Range
Storage . . . . . . . . . . . . . . . . . . . . .
S p a n / Z e r o
Screwdriver adjustments located on front
Adjustments
of unit
Required
Two Wire Current Input
Operating
7.2 VDC @ 20 mA (4-20 mA signal)
Voltages
Supply
Three Wire Voltage Input
Voltage
7-30 VDC, less than 3 mA
S i g n a l
Three Wire Voltage Input
Impedance
10 Kilohms
7800 ­
T
(A)
(T)
(D)
(R)
(F)
(C)
(E)
I
( )
2
(N)
(4)
(5)
(7)
(9)
(0)
(01)
(02)
(03)
(11)
(12)
(13)
(21)
(22)
(23)
Set Point
9 psig
15 psig
[0.6 BAR]
[1.0 BAR]
[2.0 BAR]
(60 kPa)
(200 kPa)
(100 kPa)
7.0
9.5
3
3
(.20 m /HR)
(.27 m /HR)
(.38 m /HR)
3
3
9.0 (15.3m /HR) @
120 psig, [8.0 BAR],
(800 kPa) supply &
or
9 psig, [0.6 BAR],
(60 kPa) output.
-40 F to +160 F
(-40 C to +71.2 C)
-40 F to +180 F
(-40 C to +82.2 C)
30 psig
13.5
3

Advertisement

Table of Contents
loading

Summary of Contents for Fairchild T7800

  • Page 1 Intrinsically Safe approval, including non-incendive (Division 2), on 4-20 mA units only. Non-incendive (Division 2) approval on FM voltage input units only. Figure 1. Model T7800 Standard Range Transducer Identification Number System GENERAL INFORMATION Set Point The Model T7800 Series of Electro-Pneumatic Trans­...
  • Page 2: Hazardous Area Classification

    Specifications (continued) Non-Incendive: (4-20 mA and voltage input units) Performance Specifications (TDFI7800, TAFI7800, TDFN7800, TAFN7800) 0.25% Full Scale Guaranteed Accuracy Class I, Division 2, Groups A, B, C and D; 0.15% Full Scale Typical (ISA S51.1) Class II, Division 2, Groups F, and G; Class III, Division 2;...
  • Page 3: Installation

    ATEX Directive- Special Conditions for Safe Use The enclosure is manufactured from aluminum alloy. In rare You can mount the Model T7800 on a flat surface using two cases, igntion sources due to impact and friction sparks 10-32 Screws. For more information, see Figure 2.
  • Page 4 Installation (continued) Figure 4. TT7800 Outline Dimensions Figure 5. TD7800 Outline Dimensions Figure 6. TR7800 Outline Dimensions...
  • Page 5 Figure 7. Din Rail Mounting Kit 16893-1 (included with unit) Figure 8. Optional Mounting Kit 19254-1 (sold separately)
  • Page 6 Pneumatic Connections Electrical Connections Clean all pipelines to remove dirt and scale before installa­ Make connections to the Terminal Block, Conduit Connec­ tion. tor or the DIN Connector as shown in Figure 9. Apply a minimum amount of pipe compound to the male Wiring in Hazardous Areas threads of the air line only.
  • Page 7: Full-Range Operation

    SPLIT-RANGE OPERATION CALIBRATIONS / ADJUSTMENTS Lo/Hi Span Adjustment Equipment Required for Calibration 1. Set the Lo/Hi Span switch to the Lo position for 3-9 • Pneumatic supply capable of delivering up to 120 psig psig or 9-15 psig output range and for 4-20 mA input •...
  • Page 8 Calibrations / Adjustments (continued) Figure 10. T7800 Calibration Configuration...
  • Page 9 COMPONENTS Table 5. T7800 Transducer Components Item Qty. Description Cover, Machining Screw Screw Gasket Nozzle Body Assembly Orifice Assembly Spring Disk Diaphragm Spacer Ring Diaphragm Assembly Foam Block Valve Body Assembly Screw Pintle Spring, PIntle O-Ring Plug Screw 19267-1 Service Kit Components.
  • Page 10: Maintenance

    The information set forth in the foregoing Installation, Operation and Maintenance Instructions shall not be modified or amended in any respect without prior written consent of Fairchild Industrial Products Company. In addition, the information set forth herein shall be furnished with each product sold incorporating Fairchild's unit as a component thereof.