KEYS USED FOR THE SETPOINT ADJUST OVERRIDE
SETPOINT ADJUST
This override is useful in situations where the occupied
space feels too cool or warm for the occupants and a
temporary change of setpoint would make the temperature
more comfortable. It can be called from either the Occu-
pied or Unoccupied modes and functions in this way:
- Press the 3 HOUR OCCUPIED key. If in Unoccupied.
the thermostat will go to the Occupied mode, controlling
the space temperature to the Occupied setpoints for 3
hours. If in Occupied mode, no change of setpoints will
occur. However, this will ensure 3 hours of Occupied set-
point control regardless of any Unoccupied Start Times
that may be programmed. The indicator on the left side of
the display will point to 3 HR OCCUPIED while this over-
ride is in effect.
THEN:
- Press the the + key. This will adjust the setpoint up by
a preprogrammed "Amount of Setpoint
example, Occupied Heat is set for 70 F and "Amount of
Setpoint Adjust" is set for 5 F. After the + key is pressed,
the Occupied Heat setpoint will be 70 + 5 or 75 F. The
thermostat will then control the space temperature to 75 F
and the indicator on the left side of the display will
continue to point to 3 HR OCCUPIED during the
remainder of the 3 hours of adjusted setpoint.
OR
- Press the - key. This will adjust the setpoint down by a
preprogrammed "Amount of Setpoint
example, Occupied Heat is set for 70 F and "Amount of
Setpoint Adjust" is set for 5 F. After the - key is pressed,
the Occupied Heat setpoint will be 70 5 or 65 F. The
thermostat will then control the space temperature to 65 F
and the indicator on the left side of the display will
continue to point to 3 HR OCCUPIED during the
remainder of the 3 hours of adjusted setpoint.
NOTE:
Refer to the section titled TO SET THE AMOUNT OF SET-
POINT ADJUST for instructions on how to vary the
adjust.
U
Adjust". As an
Adjust". As an
15