Programmable thermostat for conventional/heat pump system
Hide thumbs Also See for T7351:

Advertisement

T7351 Programmable Thermostat
FOR CONVENTIONAL/HEAT PUMP SYSTEMS
63-2652

Advertisement

Table of Contents
loading

Summary of Contents for Honeywell T7351

  • Page 1 T7351 Programmable Thermostat FOR CONVENTIONAL/HEAT PUMP SYSTEMS 63-2652...
  • Page 2 • Individual heat and cool setpoints • Auxiliary subbase contact typically available for Occupied and Not Occupied interface with a Honeywell Economizer periods. System (for total rooftop control • Convenient overrides allow temporary integration) or act as dehumidification setpoint changes.
  • Page 3: Using Thermostat Keys

    SETTINGS Using Thermostat Keys NOTE: See Fig. 1 for keypad information. The thermostat keys are used to: Setting Temperature • set current time and day, • program times and setpoints for heating and Refer to Table 1 for default temperature cooling, setpoints.
  • Page 4: Setting System And Fan

    Setting System and Fan Fan Settings — On: Fan operates continuously in occupied System default setting is Auto. The fan default and standby periods. Fan cycles with call for is set so the fan operates continuously during: heat or cool during not occupied periods. —...
  • Page 5 The thermostat can be set for two Occupied IMPORTANT and two Not Occupied times for each day of the Programming the thermostat with the week (28 independent time settings). The keypad requires 24 Vac (turn on Temporary Occupied key provides quick system power).
  • Page 6 Table 2. Occupied and Not Occupied Period Start Times. Occupied Not Occupied Occupied Not Occupied Period 1 Period 1 Period 2 Period 2 Monday Tuesday Wednesday Thursday Friday Saturday Sunday NOTE: 12:00 PM is Noon, and 12:00 AM is Midnight. 63-2652...
  • Page 7 Temperature Set Day/Time Override Temporary Temporary Occupied Not Occupied Occupied Not Occupied Time HEAT COOL HEAT COOL Schedule System Clear Schedule Occupied Not Occupied Start Time Copy ON AUTO HEAT COOL M19610BB Fig. 1. Thermostat key locations. When using the keypad to change the day/time: Fri = Friday, Sat = Saturday.
  • Page 8: Setting Schedule Times

    Copying a Day 4. Press Run Schedule. Use the keys in the “Schedule” area of the Setting Schedule Times keypad for this procedure. Use the keys in the “Schedule” area of the NOTE: The thermostat must be in program keypad for this procedure. mode to use the copy feature.
  • Page 9: Clearing Program Start Times

    Temperature Setpoints 7. Repeat steps 2 through 6 for all the days desired. 8. Press Run Schedule. Setpoint Limits The setpoint temperature range is 40 to 90 °F Clearing Program Start Times (4 to 32 °C) for heating and 45 to 99 °F (7 to 1.
  • Page 10: Temperature Setpoint Overrides

    T7770 Setpoint Knob 6. Press up ! or down " until the desired temperature is displayed. A T7770 setpoint knob can remotely adjust the 7. Press Not Occupied Cool. T7350 setpoint. This adjustment can be made 8. Press up ! or down " until the desired when the sensor is in override.
  • Page 11 1. To use the default occupied override, NOTES: press Temporary Occupied. — If the number of days is set to zero, no temporary change takes effect. NOTE: The default temperature setting — If the number of days is set just is the Occupied setpoint.
  • Page 12: Changing Temperature Setpoint Until Next Program Period

    By using this Honeywell literature, you agree that Honeywell will have no liability for any damages arising out of your use or modification to, the literature. You will defend and indemnify Honeywell, its affiliates and subsidiaries, from and against any liability, cost, or damages, including attorneys’ fees, arising out of, or resulting from, any modification to the literature by you.