Dear users, Thank you for choosing our product ! Important Safety Instructions Please keep this manual for future review. This manual contains all instructions of safety, installation and operation for Tracer Dream 200V series Maximum Power Point Tracking (MPPT) controller ("the controller" as referred to in this manual). General Safety Information ①...
Page 3
◼ Auto-control of utility and generator dry contact design to compose a hybrid power system easily ◼ Power reduction automatically over temperature range ◼ TVS lighting protection. ◼ Support parameters setting via the iConnect App 1.2 Characteristics ①Ldsolar logo ② LCD with backlight ③ Menu ④ up ⑤Down ⑥...
The controller is designed with a common negative polarity. The negative polarity of the PV and the battery is located on the same busbar. Connect an RBVS (Remote Battery Voltage Sensor) to detect accurate battery voltage. The sampling distance is no longer than 20m. Connect an RTS (Remote Temperature Sensor) to remotely detect the battery temperature.
Page 5
Input power (Ppv)= Output power Input voltage (V ) *input current (I ) =Battery voltage (V ) *battery current (I Normally, the V is always higher than V , Due to the principle of conservation of energy, the I is always higher than I .
Page 6
1.5 Battery Charging Stage The controller has a 3 stages battery charging algorithm (Bulk Charging, Boost Charging and Float Charging) for rapid, efficient, and safe battery charging. Figure 1-5 Lead acid Battery Figure 1-6 Li Battery charging charging stage Curve stage curve (1) Bulk Charging In this stage, the battery voltage has not yet reached boost voltage, the controller operates in constant...
1.6 Included accessories Instruction Quantity Picture accessories the standard length of the cable is 1M. Remote Temperature 1 pc Sensor 2P-3.5mm 2P-3.81mm 2 pc Dry Contact Terminal External bluetooth module (CM-B01)with1M Bluetooth Module RJ45 cable The above-included accessories are packed in a plastic bag and a box,Please check after opening the package.
Page 8
The below table is for reference only. Table 2-1 TD4620Pro/TD4820Pro/TD41020Pro 36 cell 48 cell 54 cell 60 cell System Voc<23V Voc<31V Voc<34V Voc<38V voltage Max. Best Max. Best Max. Best Max. Best 72 cell 96 cell Thin-Film Voc<46V...
Page 9
Table 2-2 maximum power of PV array for this controller Max. PV open circuit Model Rated Charge Current Rated Charge Power Max. PV Array Power voltage 800W/12V 1200W/12V TD4620Pro 1600W/24V 2400W/24V 3200W/48V 4800W/48V 1500W/12V 1000W/12V ℃) 180V(25 2100W/24V...
Page 10
2.4 Dry Contact Instruction Dry contact parameter Rated Value:3A/30VDC Maximum Value:0.5A/60VDC Battery Voltage (V Low Voltage Disconnect Voltage(V Low Voltage Reconnect Voltage(V ①V < V : The dry contact controls the load to connect ②V < V : The dry contact controls the load to disconnect ③Connect an RBVS (Remote Battery Voltage Sensor) to detect accurate battery voltage.
Page 11
2.5 Mounting Warning: risk of explosion! Never install the controller and an open battery in the same enclosed space! Nor shall the controller be installed in an enclosed space where battery gas may accumulate. Warning: danger of high voltage! Photovoltaic arrays may produce a very high open-circuit voltage. Open the breaker or fuse before wiring, and be very careful during the wiring process.
Figure 2-2 Schematic of wiring diagram CAUTION: While wiring the controller do not close the circuit breaker or fuse and make sure that the leads of "+" and "-" poles are connected correctly. CAUTION: A fuse which current is 1.25 to 2 times the rated current of the controller, must be installed on the battery side with a distance from the battery not greater than 150 mm.
Page 13
3.1 Button Mode Note Short press the “OK” button can turn on/off the dry contact Dry contact ON/OFF Press the “Return” button( ↺ ) on the charging power(AH) interface Clear Fault Press the “UP”(▲)and”Down”(▼) button. Browsing Mode Long press “MENU”and”UP”(▲)for more than 5 seconds Working Record Press the “UP”(▲)and”Down”(▼) button to browse, then press “OK”...
Page 14
(2) Fault Indication Status Icon Description Battery over discharged Battery level shows empty, battery frame blink, fault icon blink Battery over voltage Battery level shows full, battery frame blink, fault icon blink Temp.icon shows Temp.inside controller is higher than 75℃, Controller over temperature temperature icon blink, fault icon blink It shows PV voltage is higher than rated PV open voltage.PV icon...
Page 15
any interface. 3.3 Setting (1) Clear the charging power(AH) Operation: Press the “Return” button( ↺ ) on the charging power(AH) interface and the value will be cleared. (2) Float Voltage Setting Operation: Step 1: At main interface(cycle display),Press “UP”(▲)and”Down”(▼) to enter float voltage interface.
Page 16
24V*2;48V*4 24V*2;48V*4 24V*2;48V*4 LF8 (LiFePO4 8S/24V*2) (Li(NiCoMn)O2 LId (Li(NiCoMn)O2 14S/48V*2) LFG (LiFePO4 16S/48V*4) 3S/12V) Over Voltage 16.0V 16.0 V 16.0 V 16.0V 17.0 V 32.0V Disconnect Charging Limited 15.0 V 15.0 V 15.0 V 14.8V 17.0 V 30.0V Voltage Over Voltage 15.0 V 15.0 V 15.0 V...
Page 17
Search for "LD iConnect" in Google Play Application market and find ldsolar's app. The icon is as follows. Just download and install it directly. · IOS for Apple Search for "LD iConnect" in the Apple store, and find ldsolar's app, with the icon above, just download and install it directly. Note: •After downloading the App, please check the application update in My iConnect --...
Please refer to the instruction manual of iConnect App for details.Scan the QR code or download from the iConnect App. 4. Protections, Troubleshooting and Maintenance 4.1 Protection When the charging current or power of the PV array exceeds the controller’s rated current or power, it will be PV current/power charged at the rated current or power.
WARNING:Risk of electric shock! Make sure that all the power is turned off before above operations, and then follow the corresponding inspections and operations. 5. Technical Specifications 5.1 Electrical Parameters Item TD4620Pro TD4820Pro TD41020Pro Auto ① System nominal voltage 12/24/48VDC...
Enclosure IP30 ◆The controller can work under full load in the working environment temperature, When the internal temperature is more than 80℃, the reducing power charging mode is turned on. 5.3 Mechanical Parameters Item TD4620Pro TD4820Pro TD41020Pro Dimension(L*W*H) 277×244×111mm 375*244*135.5mm 468*244*135.5mm...
Page 22
FCC Warnning: This equipment has been tested and found to comply with the limits for a Class B digital device, pursuant to part 15 of the FCC Rules. These limits are designed to provide reasonable protection againstharmful interference in a residential installation. This equipment generates, uses and can radiateradio frequency energy and, if not installed and used in accordance with the instructions, maycause harmful interference to radio communications.