Operation

The device is preconfigured according to the enclosed documentation. Settings such as switching on and switching off
temperature limits can be adjusted. The OPA-S operating/programming unit is used for configuration. This can also be
used to display the measured values (see section "TOA Configuration", page 8).
Thermostat function
OFF Limit > ON Limit (standard setting)
The following diagram shows the temperature-dependent
switching behavior of the TOA output voltage for the
standard OFF / ON setting of 35 °C / 30 °C (95 °F / 86 °F).
OFF Limit IP 03 > ON Limit IP 04
(standard setting)
TOA output
Signal LED
ON
LED green
OFF
LED red
30
86
Signal LED
The signal LED on the top of the housing indicates the operating status of the TOA.
LED
Status
red
Output is off
green
Output is on
green flashing
Device startup
red flashing
Sensor error
(2 sec. cycle)
green red
Output error
repeated flashing
dark
No power
Signal LED
Doc: 70-00-0851A V1.0, 20210716
Subject to change without notice
Switching ON temperature
limit parameter IP 04
Switching OFF temperature
limit parameter IP 03
T [°C]
35
95
T [°F]
© Vector Controls GmbH, Switzerland
www.vectorcontrols.com
OFF Limit < ON Limit
The following diagram shows the temperature-dependent
switching behavior of the TOA output voltage for an OFF /
ON setting of 20 °C / 25 °C (68 °F / 77 °F).
OFF Limit IP 03 < ON Limit IP 04
TOA output
Signal LED
ON
LED green
OFF
LED red
20
68
Description
The contact is opened = 0 V
TOA-T101 output voltage = 24 V AC/DC
TOA-T102 output voltage = 230 VAC
TOA is starting up.
Temperature sensor is not connect or failed.
TOA output overloaded or short circuit at output.
Device has no power or is defect
Thermostat TOA
Switching OFF temperature
limit parameter IP 03
Switching ON temperature
limit parameter IP 04
25
T [°C]
77
T [°F]
Page 7 / 10