Additional Information - Vector TOA-T101 Quick Start Manual

Table of Contents

Advertisement

Copy TOA parameters
It is possible to load TOA parameters to the memory device AEC-PM2 and copy them to other TOA
devices.
Loading memory device
1.
Remove the upper part of the TOA housing (see section "Connecting the TOA and putting it
into operation", page 6).
2.
Insert the AEC-PM2 memory device into the TOA connector P7. Ensure correct polarity (see
section "Wiring and Connection", page 4)!
3.
Connect the OPA-S operating device to the TOA connector P6 (see section "Wiring and Connection", page 4).
The measured temperature is displayed.
4.
Press the "UP" and "DOWN" keys simultaneously for at least 3 seconds and wait until "Code" is displayed.
5.
Use the "UP" or "DOWN" keys to set the password "0009" and confirm with the "RIGHT" key.
6.
Confirm the "IP SEL" display with the "RIGHT" key. The first parameter will be displayed.
7.
Use the "UP" or "DOWN" keys to switch to the "IP 05" parameter. After pressing the "RIGHT" key, use the "UP"
or "DOWN" keys to set the parameter to "1". Confirm the setting with the "RIGHT" key.
8.
After pressing the left "ON/OFF" key twice, the parameters are copied from the TOA to the AEC-PM2.
The red "Data" LED of the AEC-PM2 lights up for 5 seconds after successful copying and parameter "IP 05" is set
to 0. If copying has failed, the red "Data" LED flashes for 5 seconds and parameter "IP 05" is set to 7.
9.
Remove the AEC-PM2 memory device and the OPA-S operator interface and close the TOA housing (see section
"Connecting the TOA and putting it into operation", page 6).
Copy parameters to other TOA devices
1.
Remove the upper part of the TOA housing (see section Connecting the TOA and putting it into operation, page
5).
2.
Insert the AEC-PM2 memory device into the TOA connector P7. Ensure correct polarity (see section "Wiring and
Connection", page 4)!
3.
After pressing the "Copy" key on the AEC-PM2, the parameters are copied from the AEC-PM2 to the TOA.
The red "Data" LED of the AEC-PM2 lights up for 5 seconds after a successful copy process. If copying has failed,
the red "Data" LED flashes for 5 seconds.
4.
Remove the AEC-PM2 memory device and close the TOA housing (see section "Connecting the TOA and putting it
into operation", page 6).
Signal LED on the AEC-PM2 memory device
LED (red)
Status
lights up
successful
flashes
error

Additional Information

Conventions
The following display conventions apply to this document:
Danger
Indicates a hazard with a high degree of risk. Failure to observe this warning may result in immediate danger of
serious injury or death.
Important
Failure to comply with these warnings can result in equipment damage.
Information
Further information, important operating instructions, other details.
Reference to another document or other text passages.
Used abbreviations
Abbreviation
Meaning
NTC
Negative Temperature Coefficient
Doc: 70-00-0851A V1.0, 20210716
Subject to change without notice
Description
Copying of parameters successfully completed. LED lights up for 5 seconds.
Error while copying the parameters. LED flashes for 5 seconds.
© Vector Controls GmbH, Switzerland
www.vectorcontrols.com
Thermostat TOA
AEC-PM2
1
Page 9 / 10

Advertisement

Table of Contents
loading

This manual is also suitable for:

Toa-t10240-10024240-100243

Table of Contents