Model
Spec.
Extension interface
Panel components
Alarm LED indicator
(Red)
Power LED indicator
(Green)
Display area
Numeric keys
Function keys
Enter key (ENT)
Arrow keys
Electrical Specifications
Model
Spec.
CPU
Program memory
RAM of the system
Power supply voltage
Power consumption
Power protection
Insulation resistance
Noise immunity
Ground
Operating temperature
for hardware
Storage temperature
for hardware
Waterproof class of the
front panel
Vibration/Shock
resistance
Weight
Dimensions
Cooling method
Item
Input number
Input type
Input voltage (±10%)
Input impedance
Maximum frequency
OffOn
Action level
OnOff
OffOn
Response
time
OnOff
Slot for a program copy card
Status 1: when turning on the power, this LED will start blinking
slowly and when the power is ON, this LED will be off.
Status 2: when the user-defined conditions are met, LED will blink
every 1 second along with an alarm sound.
When the power is ON, this LED will be ON.
LCD module; it is used to display current program status.
Keys 0~9 can be used for inputting constants. Users can also define
the keys by themselves.
Users can define the keys.
If the input value is correct, press the key to confirm the setting.
Users can define the key in the user page.
Up: for increasing the setting value or go to the previous page
Down: for decreasing the setting value or go the next page
Left/Right: for selecting the position of the setting value
Users can redefine functions of the arrow keys in the user page.
TP04P-
16TP1R/T
LPC1787FBD208
1 MB-flash memory
64K Bytes
24VDC (-15% ~ 20%) (With counter-connection protection on the
polarity of DC input power)
3W / 2.5W
With counter-connection protection on the polarity of DC input power
> 5 MΩ (all I/O point-to-ground insulation resistance: 500 VDC)
ESD (IEC 61131-2, IEC 61000-4-2): 8KV Air Discharge
EFT (IEC 61131-2, IEC 61000-4-4): Power Line: 2KV, Digital I/O:
1KV, Analog & Communication I/O: 1KV
Damped-Oscillatory Wave: Power Line: 1KV, Digital I/O: 1KV
RS (IEC 61131-2, IEC 61000-4-3): 26MHz~1GHz, 10V/m
The diameter of ground cannot be less than the diameter of the
power cable. (If several TP04P are used, they should be grounded
directly.)
0°C~50°C: Relative humidity: 20%-90% RH (non-condensing)
-20°C~60°C
IP66/NEMA4
International standards IEC61131-2, IEC 68-2-6 (TEST Fc)/
IEC61131-2 & IEC 68-2-27 (TEST Ea)
420g
175.8 × 108.6 × 59.2 mm (Width(W) × Height(H) × Deep(D))
Natural air cooling
Model
24VDC (-15% ~ 20%) single common terminal
TP04P series
Description
TP04P-
32TP1R/T
5W / 4.5W
444g
Input terminal
X0, X1
DC (Sinking or sourcing)
24VDC, 5mA
4.7k ohm
10KHz
> 16.5 VDC
< 8 VDC
<20us
<50us
- 3 -
TP04P-
22XA1R/T
21EX1R/T
4.7W / 4.5W
4.7W / 4.5W
432g
X2~X7, X10~X17
60Hz
10ms
TP04P-
432g