TECSYSTEM S.r.l ® 1) TECHNICAL SPECIFICATIONS POWER SUPPLY COMMUNICATION: ONLY FOR T2612 AND T2612AD • Rated voltage 120 or 240 Vac 50/60 Hz • Standard serial output RS485 Modbus® • Selection through voltage jumper • Tolerance +/- 10% • Power input protected by 500 mA fast...
Channel 2 must be always referred to the central column of the transformer. Channel 4 must be always referred to the ambient Pt100 sensor, if you want to monitor the temperature of the transformer box through the T2612 unit. 6) PT100 EXTENSION CABLE: TECHNICAL SPECIFICATIONS Cable 20xAWG 20/19 Cu/Sn Section 0.55 mm²...
Page 4
• have tinned or silvered conductors All the “T” series units have the sensors linearization with a max error of 1% v.f.s.. TECSYSTEM srl has realised a special cable for the measure signal transport with all the protection requirements according to CEI Norms: mod. CT-ES...
TECSYSTEM S.r.l ® 11) COOLING-FAN CONTROL The T2612 unit, if suitably programmed, can control the ON/OFF of the transformer fans according to the set temperature values. The fans of the machine can be controlled in two different ways: • using the temperatures surveyed by the sensors on the three columns CHF 1 2 3 - CH4 excluded ALARM and TRIP LED 1.2.3 illuminated (e.g.
Page 6
Exclusion system is automatically disconnected when the temperature goes under the ALARM threshold. 19) BUZZER T2612 unit includes a buzzer that is operating when any alarm status occurs, except for Fan 1 and Fan 2 outputs By pushing the TEST/MUTE key you can stop the buzzer.
Page 7
Enter HLd YES or NO Prg NO= program cannot be PRG/SET PRG appears on display changed set up Prg YES or NO ONLY for T2612 and T2612-AD, PRG/SET Adr appears on display not for T2612-B and T2612-C enter the address of the unit PRG/SET...
22) RULES FOR WARRANTY The Product purchased is covered by manufacturer's warranty or the seller's terms and con- ditions set forth in the "General Conditions of Sale Tecsystem srl", available at www.tecsystem.it and / or purchase agreement. The warranty is considered valid only when the product will be damaged by causes attribu- table to TECSYSTEM srl, such as manufacturing or components defects.
TECSYSTEM S.r.l ® TROUBLESHOOTING PROBLEMS CAUSES / SOLUTIONS Check the terminal block for correct instal- The unit will not switch on, lation. with control power energized. Check for voltage at the terminal block. Channel 4 is indicating fault and displaying Wrong programming of the unit.
The T2612 implements a sub-whole of the standard serial communication protocol Modicon Modbus RTU. The Modbus T2612 employs a RS485 connection with 2 twisted-pair wire hardware; with this mode it is allowed to connect up to 32 monitoring units on the same wiring.
Page 11
(10) EXCEPTION CODE: Exception responses In case of wrong questions, the T2612 answers with modified codes and codified errors ac- cording to the following: Packet of error answer : Slave address, Function code (+bit 7 to 1), Exception code, CRC-Hi, CRC-Lo...
TECSYSTEM S.r.l ® CUTOUT FRONT VIEW Screw rivet Screw rivet M3 x 15mm M3 x 15mm Cut out: 155 X 280 mm Screw rivet Screw rivet M3 x 15mm M3 x 15mm 190 mm 210 mm GALVANIZED SHEET IRON Thickness 1.2 mm...