Connect the negative (black) lead to the negative battery terminal.
2.
NOTE: A small amount of arcing may occur when connecting the batteries. This is normal and does not
damage the unit or present any safety concern.
Replace the UPS front bezel.
3.

Selecting the UPS voltage configuration

Using a small tool, position the DIP switches according to the desired voltage configuration as identified
on the rear panel of the UPS and in the following table.
NOTE: An asterisk (*) indicates the default setting.
T750 NA/JPN
Output voltage
Input voltage range
100 V
90–106 V
110 V
99–116 V
120 V
108–127 V
DIP switch 2
DIP switch 1
Down
Up
Up
Down
Up
Up
Installation 11