T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT
Using Temporary Occupied Override
The Temporary Occupied Override can be used when the
T7350 is in Not Occupied or Standby mode. It switches to the
Occupied mode for a fixed number of hours.
1. To use the default occupied override, press Temporary
Occupied.
NOTE: The default temperature setting is the
Occupied setpoint.
2. To select a temperature setting other than the default,
press up
or down
offset is displayed (range is 0°F to 3°F).
NOTE: This offset can be restricted by the limits
detailed in the Setpoint Limits section.
Using Temporary Not Occupied Override
The Temporary Not Occupied Override fixes the device to
operate in Not Occupied mode for a number of days (between
1 and 99) without changing programming saved in memory.
63-2605—2
until the desired temperature
NOTES:
If the number of days is set to zero, no temporary
change takes effect.
If the number of days is set just below zero, the
display for days is "---" (an indefinite override).
To turn off this override, you must press Run
Schedule.
1. Press Temporary Not Occupied.
2. Press up
the Not Occupied period (in days).
NOTE: The default temperature setting is the
Not Occupied setpoint.
3. Press
to display the default setpoint.
NOTE: The only way to change this setpoint is to
change the Not Occupied setpoint.