Fujitsu SPARC T5440 User Manual page 78

Hide thumbs Also See for SPARC T5440:
Table of Contents

Advertisement

Fixed ILOM Issues (Continued)
TABLE A-3
CR ID
Description
6902381
When you powered on the server, all LEDs or all
LEDs on the right side on the front panel may
light up. When using System Firmware 7.2.2.e or
later, the ILOM status check command (the
showenvironment command) also displays the
status of relevant LED being ON; however, this
event itself is an issue absolutely limited to the
LED display and does not have an effect on the
system.
6947945
When you mount a Fujitsu 4Gbps Fibre Channel
card and start the system, the 4Gbps Fibre
Channel card is falsely recognized as a F20 card
in the ILOM CLI interface. Also, the slot number
is falsely displayed. In addition, the false
recognition and the false display may occur also
in the FRU Status of the prtdiag -v command
output.
For details, see
Card Is Falsely Recognized as F20 Card (CR
6947945)" on page
6948710
With System Firmware 7.2.7.b or later, messages
referring to hot insertions/removals of devices
(including a nonexistent device) may be
displayed intermittently during the system
startup and the system running.
Message example of a nonexistent device:
Chassis | major: Hot insertion of
/SYS/MB/RISER1/XAUI1
Chassis | major: Hot removal of
/SYS/MB/RISER1/XAUI1
Message example of an existent device:
Chassis | major: Hot removal of
/SYS/MB/CMP0/BR1/CH0/D0
Chassis | major: Hot insertion of
/SYS/MB/CMP0/BR1/CH0/D0
68
SPARC Enterprise T5440 Server Product Notes • December 2010
"Fujitsu 4Gbps Fibre Channel
75.
Workaround
Note - Fixed in System Firmware 7.2.10 or later.
None.
When this event occurred, perform the ILOM
reset operation. If not recovered, shut down the
system and then remove and insert the power
cord.
ILOM reset operation example:
Log in to ILOM and execute the following
command.
[In case of ILOM command mode]
-> reset /SP
Are you sure you want to reset /SP
(y/n)? y
[In case of ALOM CMT compatible shell]
sc> resetsc
Are you sure you want to reset the SC [y/n]? y
Note - Fixed in System Firmware 7.2.10 or later.
None.
The newly generated ILOM event log is
normally collected.
For details, see
"Fujitsu 4Gbps Fibre Channel
Card Is Falsely Recognized as F20 Card (CR
6947945)" on page
75.
Note - Fixed in System Firmware 7.2.10.a or
later.
None.
ILOM firmware's way of referring to the sensor
is wrong. This has no impact on the system. If no
faults are detected by the show faulty
command, ignore the output messages.

Advertisement

Table of Contents
loading

Table of Contents