CONNECTING TO A VENTILATION DUCT (T701/T731/T761)
You will need a UL-CSA-approved, 4-inch ridged metal
exhaust duct.
NOTE: The more bends and the longer the duct, the
less air will circulate through the machine,
which will impede drying performance. We rec-
ommend that you cut off any excess exhaust
duct and run the duct with as few bends as
possible. And make any necessary bends as
gentle as possible.
NOTE: Maximum duct length of 22 feet is allowed.
Subtract 4 feet of duct for each 90° elbow.
If more than 20 feet of duct is needed, the diameter
must be increased to 6" or 8" (152 mm or 203 mm).
NOTE: When installing in warm climates (77° F and
above) with high humidity levels, do not
route the air exhaust duct upwards.
Installation Examples
CONDENSATION DRAIN CONNECTION (T721 AND T781)
If possible, you should install the dryer so the condensed
water will continuously flow into a drain or sink. To do
this, follow the instructions below:
1. Disconnect the short hose (1) from the blue
connection. (It's okay to let the hose hang down.)
2. Connect the rubber hose supplied with the dryer to
the blue nipple (2).
3. Run the hose to a drain or sink, as illustrated.
NOTE: The drain hose must not be more than 40"
above the floor.

LEVELING THE MACHINE

It is important that the machine is level. Each foot on
the dryer is adjustable, so you can level the unit on any
surface. Once it is level, securely tighten the lock nuts
on the feet.
Subtract 4 feet (122
cm) for every 90°
elbow.
To connect the exhaust duct to a ventilation outlet, follow
the steps below:
1. Connect the exhaust duct to a ventilation exhaust
fitting or to a discharge through the wall.
2. Secure the duct joint to the outlet stub on the machine.
3. Run the duct with as few bends as possible to the
point of discharge.
WARNING!
This appliance should not be exhausted into a chimney, a
wall, a ceiling, or a concealed space of a building. Only a
metal ventilation grill should be used.
If the duct is taken to a wall outlet, a ventilation grill
should be fitted to prevent reverse flow of cold air. Fit
the ventilation grill to the outside or inside of the wall.
Ventilation grill
Make sure nothing is blocking the
ventilation grill.
Vent spacer
2
1
3
Back of dryer
If there is only one
vent duct from the
room, a vent spacer
must be fitted.
3
Be sure to tighten the lock
nuts securely when you
level the machine.
Page 5