2 - Appendix
2.1 Adjusting Water Flow Using ΔT (Delta-T)
The Delta-T is the temperature difference between the water temperatures entering and leaving the heat
pump.
The equipment can be fine-tuned for maximum performance by balancing water flow rates to maintain an
ideal ∆T.
The adjustment procedure must be completed with the unit in heating mode
1. Adjust the thermostat to its lowest setting with the unit in heating mode.
2. Deactivate the water filtration pump.
3. Confirm that the filters leading to the heat pump are clean.
4. Adjust the valves controlling water headed towards the heat pump to the half-open position.
5. Adjust the valves controlling water leading away from the heat pump to a fully open position.
6. Activate the pool water filtration pump.
7. Slowly raise the thermostat temperature until the heat pump activates.
After a four-minute delay, the heat pump's compressor will start.
l
8. With the heat pump running, confirm the filtration pump is operating properly with adequate flow and no short
cycling.
9. Wait for water temperatures to stabilize (approximately 5 minutes).
10. Adjust valves in the following order using the temperature chart provided.
a. Adjust the valve that controls water exiting the heat pump until the correct temperature differential is achieved.
Match the temperature measured with a temperature probe to the chart.
b. Wait for water temperatures to stabilize. Then check the temperature again. Re-adjust the valve as needed.
11. Mark valves at these positions for future reference.
HEAT EXCHANGER
TYPE
Titanium ThermoLink
Table 2 - Temperature Chart
Page - 15
IN THIS SECTION:
2.1 Adjusting Water Flow Using ΔT (Delta-T)
2.2 Adjusting Water Pressure Switch (Select Units)
2.3 Clearances
2.4 Cleaning Equipment After Installation
2.5 Dimensions
2.6 Identifying Model Specifications
2.7 Weights
2.8 Initial Heating Recommendations
2.9 Winterizing
2.10 Available Accessories
MODEL
®
T030
TEMPERATURE
1° to 4° F
(.5° C to 2.2° C)
15
16
18
18
20
20
20
21
21
22