6. Start and Shutdown

6.1 Start-up procedure

To start-up the inverter, it is mandatory that the steps below are followed in the exact order
outlined.
1). Ensure the commissioning checks in Section 5 have been performed.
2). Switch the AC switch ON.
3). Switch the DC switch ON. If the PV array (DC) voltage is higher than the inverter's
start-up voltage, the inverter will turn on. The red DC POWER LED and LCD will be
continuously lit.
4). Canadian Solar inverters are powered from the DC side. When the inverter detects DC
power that is within start-up and operating ranges, the inverter will turn on. After turn-
on, the inverter will check internal parameters, sense and monitor AC voltage, hertz
rate and the stability of the supply grid. During this period, the green OPERATION LED
will flash and the LCD screen will show INITIALIZING. This tells the operator that the
inverter is preparing to generate AC power.
5). After the locally mandated delay (300 seconds for IEEE-1547 compliant inverters), the
inverter will start generating AC power. The green OPERATION LED will light
continuously and the LCD screen will show GENERATING.
CAUTION
The inverter's surface temperature can reach up to 75℃ (167 F). To
avoid risk of burns, do not touch the surface when the inverter is in
the operational mode. Additionally, the inverter must be installed
out of the reach of children.

6.2 Shutdown procedure

To stop the inverter, it is mandatory that the steps below are followed in the exact order outlined.
1). Switch AC switch OFF.
2). Wait approximately 30 seconds (during this time, the AC side capacitors are dissipating
energy). If the inverter has DC voltage above the start-up threshold, the red POWER
LED will be lit. Switch the DC switch OFF.
3). Confirm all LED's switch OFF (~one (1) minute).
CAUTION
Although the inverter DC disconnect switch is in the OFF position and all
the LED's are OFF, operators must wait five (5) minutes after the DC power
source has been disconnected before opening the inverter cabinet. DC
side capacitors can take up to five (5) minutes to dissipate all stored energy.
.32.

7. Normal Operation

In normal operation, LCD screen alternatively shows inverter power and operation status
(see Figure 6.1). The screen can be scrolled manually by pressing the UP/DOWN keys.
Pressing the ENTER key gives access to Main Menu.
Power
01-01-2019
5 sec
UP/DOWN or
Start
auto-scroll
(10 sec)
Status: Generating
01-01-2019
Pressing the
ENTER key
gives access to
the main menu.
Figure 7.1 Operation Overview

7.1 Main Menu

There are four submenus in the Main Menu (see Figure 6.1):

1. Information

2. Settings
3. Advanced Info.
4. Advanced Settings
7.2 Information
The Canadian Solar three Phase Inverter main menu provides access to operational
data and information. The information is displayed by selecting "Information" from the
menu and then by scrolling up or down.
Pressing the
Main Menu
ESC key
calls back the
previous menu.
Information
110000W
UP/DOWN
12:04
Settings
UP/DOWN
Advanced Info.
UP/DOWN
12:04
Advanced settings
.33.