Typical Through The Wall - Napoleon TIMBERWOLF PEDESTAL T2250 Installation And Operating Instructions Manual

Table of Contents

Advertisement

Available languages

Available languages

4.1.4 TYPICAL THROUGH THE WALL

If possible, design the installation so that the connector does not pass through a combustible wall. If during
your installation you must pass through a combustible wall, check with your building inspector before you
begin. Also check with the chimney connector manufacturer for any specifi c requirements.
Consult with your dealer regarding special connection components available for use for wall pass-throughs.
Use only parts that have been tested and listed for use in a wall pass-through.
COMBUSTIBLE
OUTSIDE WALL
SECTION
LISTED
CHIMNEY PIPE
TO
STOVE
THIMBLE
LISTED
CHIMNEY
2" (50.8mm)
CLEARANCE
INSULATED
"T"
WALL
SUPPORT
WALL SPACER
FOR OUTSIDE
WALL
PROTECTOR
MAINTAIN 2"
ROOF
(50.8mm) CLEARANCE
THROUGH EAVE
COMBUSTIBLE
CEILING
CHIMNEY
CONNECTOR
FLOOR
53
TERMINAL
STORM
COLLAR
FLASHING
COMBUSTIBLE
WALL
61.1A
W415-1212 / 05.13.13
EN

Advertisement

Table of Contents
loading

Table of Contents