Main Menu Buttons -
General Setup

Language

English
Spanish/Español
French/Français
Smart Recovery - OFF
Smart Recovery - ON
Smart Recovery turns on the heat before the Occupied
start time to bring the room temperature to the Occupied
setpoint at the start of the Occupied time period. Please
allow 4-8 days for Smart Recovery time to adjust. When
used with a heat pump, electric strip heat will be disabled
while Smart Recovery is active.

Installation Settings

Heat & Cool Stages
Heat & Cool Stages
Up to 2 Stages Cooling and 4 stages Heating.

Compressor Stages

Up to 2 compressors.

Aux Heat Stages

0 to 2 stages of Aux Heating.
Timers & Deadbands
Cycles Per Hour
At 6 cycles per hour, the HVAC unit will only be allowed to energize
once every 10 minutes. The Cycles Per Hour limit may be overridden
and reset by pressing the WARMER or COOLER buttons.
(2, 3, 4, 5, 6, No Limit)
Settings
(en)
(1h1c)
(1h1c)
}
(1h1c)
(1h1c)
(6)
43
(Continued)
Only available when
dip switch is set for
Heat Pump operation.