TCF T050 Instructions Manual

Ceiling exhaust fan

Advertisement

Quick Links

CEILING EXHAUST FAN
READ AND SAVE THESE INSTRUCTIONS
WARNING
TO REDUCE THE RISK OF FIRE, ELECTRIC SHOCK, OR INJURY TO PERSONS,
OBSERVE THE FOLLOWING:
1. Use this unit only in the manner intended by the manufacturer. If you have questions,
contact the manufacturer at the address or telephone number listed in the warranty.
2. Before servicing or cleaning unit, switch power off at service panel and lock the
service disconnecting means to prevent power from being switched on accidentally.
When the service disconnecting means cannot be locked, securely fasten a promi-
nent warning device, such as a tag, to the service panel.
3. Installation work and electrical wiring must be done by a qualified person(s) in
accordance with all applicable codes and standards, including fire-rated construc-
tion codes and standards.
4. Sufficient air is needed for proper combustion and exhausting of gases through the
flue (chimney) of fuel-burning equipment to prevent backdrafting. Follow the heating
equipment manufacturer's guideline and safety standards such as those published
by the National Fire Protection Association (NFPA), and the American Society for
Heating, Refrigeration and Air Conditioning Engineers (ASHRAE), and the local
code authorities.
SCREWDRIVER
SLOT
1. Remove motor plate from housing by pushing down on rib in plate
while pulling out on side of housing. Motor plate may also be
removed by inserting a straight-blade screwdriver into slot in
housing and twisting screwdriver.
2. Remove wiring cover from housing by pulling straight out. Unit is
shipped ready to wire through the top of housing. To wire through
the side, bend housing flap to cover top hole and expose side hole.
DO NOT BREAK OFF FLAP. If flap breaks, plug unused hole
using standard electrical hole plug.
INSTALLATION
WIRING
COVER
HOUSING
FLAP
MODEL T050 • T050EX
WARNING
5. When cutting or drilling into wall or ceiling, do not damage electrical wiring and other
hidden utilities.
6. Ducted fans must always be vented to the outdoors.
7. This unit may be used over a tub or shower enclosure when installed in a GFCI
protected branch circuit.
8. If this unit is to be installed over a tub or shower, it must be marked as appropriate for
the application.
9. Never place a switch where it can be reached from a tub or shower.
10. This unit must be grounded.
CAUTION
1. For general ventilating use only. Do not use to exhaust hazardous or explosive
materials and vapors.
2. To avoid motor bearing damage and noisy and/or unbalanced impellers, keep
drywall spray, construction dust, etc. off power unit.
3. Please read specification label on product for further information and require-
ments.
HOUSING
GROUND
WIRECLIP
DETAIL
3. Turn off electrical power at service entrance and connect
power cable to housing using appropriate connector. Wire black
to black, white to white. Insert ground wire into grounding clip and
secure to emboss in housing. Push all wiring up into corner of unit
and replace wiring cover. Make sure cover holds housing flap in
place against side or top of housing. CAUTION: DO NOT ALLOW
WIRES TO EXTEND OUTSIDE OF WIRING BOX. Wire left
exposed will become pinched or cut when motor plate is
installed. Electrical shock may result.
4. Choose the location for your fan. For best performance, use the
shortest possible duct run and a minimum number of elbows. For
wall installations: Position unit so damper flap closes when unit is
off.
5. Use embossed measuring guides on side of housing to position
housing for proper wall or ceiling thickness. MAKE SURE HOUS-
ING WILL BE FLUSH WITH FINISHED CEILING OR WALL. Nail
housing or stude joist using four nails to ensure a solid, quiet
installaltion.
RECEPTACLE
SWITCH BOX
LINE IN

Advertisement

Table of Contents
loading
Need help?

Need help?

Do you have a question about the T050 and is the answer not in the manual?

Questions and answers

Subscribe to Our Youtube Channel

Summary of Contents for TCF T050

  • Page 1 MODEL T050 • T050EX CEILING EXHAUST FAN READ AND SAVE THESE INSTRUCTIONS WARNING WARNING TO REDUCE THE RISK OF FIRE, ELECTRIC SHOCK, OR INJURY TO PERSONS, 5. When cutting or drilling into wall or ceiling, do not damage electrical wiring and other OBSERVE THE FOLLOWING: hidden utilities.
  • Page 2 PART NO. DESCRIPTION 99110752 Grille Only 99140137 Grille Springs (2 Required) 97009346 Grille Assembly (Includes Key Nos. 1 & 2) 99080254 Motor (T050) 99080265 Motor (T050EX) 98006791 Motor Plate 99110655 Blower Wheel 99260428 Nut #6-32 (2 Required) 97008632 Damper/Duct Connector...
  • Page 3 MODELS • T080 • T080EX Page 1 CEILING VENTILATOR READ AND SAVE THESE INSTRUCTIONS WARNING WARNING TO REDUCE THE RISK OF FIRE, ELECTRIC SHOCK, OR IN- 6. Ducted fans must always be vented to the outdoors. JURY TO PERSONS, OBSERVE THE FOLLOWING: 7.
  • Page 4 MODELS • T080 • T080EX Page 2 TYPICAL INSTALLATIONS INSTALL THE HOUSING (continued) (continued) New Construction 4" ROUND DUCT POWER CABLE MOUNTING HOUSING SUSPENDED GRILLE CEILING MATERIAL SUSPENDED CEILINGS 3. Set housing aside and drive nails partially into joist at the top of both keyhole marks.
  • Page 5 MODELS • T080 • T080EX Page 3 INSTALL THE HOUSING CONNECT THE WIRING (continued) SCHEMATIC WIRING DIAGRAM B L K B L K Existing Construction O N / O F F S W I T C H W H T B L K L I N E W H T...
  • Page 6 MODELS • T080 • T080EX Page 4 WARRANTY USE AND CARE WARNING: DISCONNECT ELECTRICAL POWER SUPPLY AND Limitation of Warranties and Claims LOCK OUT SERVICE PANEL BEFORE CLEANING OR SERVIC- Seller warrants to the original purchaser that the goods sold hereunder shall be ING THIS UNIT.
  • Page 7: Table Of Contents

    T080E T110E READ AND SAVE THESE INSTRUCTIONS ENERGY STAR ® Installer: leave this guide with homeowner. Multi-Speed Ventilation Fan INSTALLATION GUIDE Table of Contents Warnings and Cautions Typical Installation New Construction Installation Easy installation in both Retrofit Installation Operation new construction and retrofit Cleaning and Maintenance Troubleshooting Service Parts...
  • Page 8: Warnings And Cautions

    Page 2 T080E T110E Installation Guide WARNING CAUTION TO REDUCE THE RISK OF FIRE, ELECTRIC SHOCK, OR . For general ventilating use only. Do not use to exhaust INJURY TO PERSONS, OBSERVE THE FOLLOWING: hazardous or explosive materials and vapors. 1.
  • Page 9: New Construction Installation

    Page 3 T080E T110E Installation Guide New Construction Installation Tools needed Materials needed • Power screwdriver with a Phillips bit • 6" round metal ducting recommended for best performance. Use of other ducting is acceptable but may impact performance. • Phillips screwdriver •...
  • Page 10 Page 4 T080E T110E Installation Guide New Construction Installation Snap-in and Secure Housing Position Housing between joists and crimp channel on both sides of Mounting Frame to lock Housing in place. Do not crimp Housing. Screws from Parts Bag Attach Duct Connector and Ducting Top and bottom flanges Screw from go outside Housing...
  • Page 11 Page 5 T080E T110E Installation Guide New Construction Installation Connect Wires and Install Knockout Plate • Run 120VAC electrical wiring to the installation location. • Use proper UL-approved connectors to secure wiring to the Knockout Plate provided in Parts Bag. •...
  • Page 12 Page 6 T080E T110E Installation Guide New Construction Installation Insert Mask and Finish Ceiling • Install ceiling material. • Cut out around Housing. Mask protects unit during construction. Remove before installing Grille. CAUTION IN ORDER TO PREVENT MOTOR/CONTROL DAMAGE: If the blower was unplugged, power must be disconnected (see page 2, WARNING item 2) before inserting motor plugs into control assembly.
  • Page 13: Retrofit Installation

    Page 7 T080E T110E Installation Guide Retrofit Installation Tools needed Materials needed • Power screwdriver with a Phillips bit • Ruler • Tape to seal duct connections • Phillips screwdriver • Pencil • Existing rigid duct will require the addition of a short length of flexible duct •...
  • Page 14 Page 8 T080E T110E Installation Guide Retrofit Installation Remove Blower Assembly Set aside Blower Assembly Both sides Remove Wiring Panel Set aside Wiring Panel Set aside screw Insert Mounting Frame Remove screws from Mounting Frame Bend up and set aside four tabs...
  • Page 15 Page 9 T080E T110E Installation Guide Retrofit Installation Secure Mounting Frame Screws set aside in Step 7 Snap-in Housing Pull existing wiring into Housing as it is inserted into Mounting Frame Attach Ducting and Duct Connector Screw from Parts Bag Pull existing ductwork into Housing...
  • Page 16 Page 10 T080E T110E Installation Guide Retrofit Installation Install Knockout Plate, Connect Wires and Reinstall Wiring Panel • Use proper UL-approved connectors to secure wiring to the Knockout Plate provided in Parts Bag. • Connect wires as shown in wiring diagram. Attach cable clamp to Knockout Plate.
  • Page 17 Page 11 T080E T110E Installation Guide Retrofit Installation Reinsert and Secure Blower Assembly CAUTION IN ORDER TO PREVENT MOTOR/CONTROL DAMAGE: Power must be disconnected (see page 2, WARNING item 2) before inserting motor plugs into control assembly. Screws from Parts Bag If ceiling repairs are needed, place Mask in Housing after Blower Assembly is secured.
  • Page 18: Operation

    Page 12 T080E T110E Installation Guide Cleaning and Maintenance WARNING Before servicing or cleaning unit, CAUTION switch power off at service panel and lock the service disconnecting means to prevent power from being IN ORDER TO PREVENT MOTOR/CONTROL DAMAGE: switched on accidentally. When the service disconnecting DO NOT remove motor plug to stop spinning motor.
  • Page 19: Service Parts

    97020845 Control Assembly & Motor (T110E) 97018331 Duct Connector - 6" 99111513 6" to 4" Reducer (Model T080E only) TWIN CITY FAN & BLOWER | WWW.TCF.COM 99020301 Blower Wheel 97019371 Scroll Assembly (T080E) 5959 Trenton Lane N | Minneapolis, MN 55442 |...
  • Page 20 MODELS • T100 • T150 T200 • T250 • T300 Page 1 CEILING / WALL-MOUNT VENTILATORS • 120V READ AND SAVE THESE INSTRUCTIONS WARNING TABLE OF CONTENTS TO REDUCE THE RISK OF FIRE, ELECTRIC SHOCK, OR IN- This manual is divided into sections as follows: JURY TO PERSONS, OBSERVE THE FOLLOWING: •...
  • Page 21 MODELS • T100 • T150 T200 • T250 • T300 TYPICAL INSTALLATION TYPICAL INSTALLATION MOUNTING (New Frame Construction) WIRING BLACK ROUND DUCT* Mounting brackets factory-shipped in BLACK TOP / BACK position for ½” OF HOUSING ceiling material. ADDITIONAL GROUND TO 1½”...
  • Page 22 MODELS • T100 • T150 T200 • T250 • T300 Page 3 MOUNTING OPTIONS DUCTING OPTIONS BLOWER DISCHARGE POSITIONS ¼-20 hex nuts secure mounting brackets to housing. Loosen and re-tighten or remove and replace nuts as necessary for desired mounting bracket position. DUCT CONNECTOR DUCT CONNECTOR 1½"...
  • Page 23 MODELS • T100 • T150 T200 • T250 • T300 Page 4 SERVICE PARTS SERVICE PARTS KEY NO. PART NO. DESCRIPTION 97014725 Housing Assembly (T100 & T150) 97014726 Housing Assembly (T200, T250, & T300) 97014728 Mounting Bracket (2 req.) 97014760 Damper Assembly (6”...
  • Page 24 Model T110 ALL INSTALLATIONS NEW CONSTRUCTION Start here. For Retrofit Installation - Skip to back page. COOKING AREA Do not install above or inside this area. 3. Attach damper/duct connector to fan housing. READ AND SAVE THESE INSTRUCTIONS Push connector through opening from inside of WARNING housing.
  • Page 25 BLACK ON / OFF SWITCH WHITE (purchase separately) GROUND SWITCH BOX (bare) TWIN CITY FAN & BLOWER | WWW.TCF.COM 5959 Trenton Lane N | Minneapolis, MN 55442 | Phone: 763-551-7600 | Fax: 763-551-7601 WIRING PLATE 99046010A 120 VAC LINE IN...
  • Page 26 MODELS T400 • T500 • T700 Page 1 Page 1 CEILING / WALL-MOUNT VENTILATORS • 120V READ AND SAVE THESE INSTRUCTIONS WARNING TABLE OF CONTENTS TO REDUCE THE RISK OF FIRE, ELECTRIC SHOCK, OR IN- This manual is divided into sections as follows: JURY TO PERSONS, OBSERVE THE FOLLOWING: •...
  • Page 27 MODELS T400 • T500 • T700 Page 2 TYPICAL INSTALLATION TYPICAL INSTALLATION MOUNTING (New Frame Construction) WIRING BLACK 10” ROUND DUCT Mounting brackets factory-shipped in BLACK TOP / BACK position for ½” OF HOUSING ceiling material. GROUND TO WIRING PLATE WIRING PLATE 4½”...
  • Page 28 MODELS T400 • T500 • T700 Page 3 MOUNTING OPTIONS DUCTING OPTIONS BLOWER DISCHARGE POSITIONS ¼-20 hex nuts secure mounting brackets to housing. Loosen and re-tighten or remove and replace nuts as necessary for desired mounting bracket position. DUCT CONNECTOR DUCT CONNECTOR 1½"...
  • Page 29 MODELS T400 • T500 • T700 Page 4 SERVICE PARTS SERVICE PARTS KEY NO. PART NO. DESCRIPTION 97014744 Housing Assembly 97014728 Mounting Bracket (2 req.) 98009449 Duct Connector 97014822 Damper Flap Assembly (2 req.) 99150415 Screw, 8-18 x ¼ (18 req.)* 98005512 Wiring Plate 99150471...
  • Page 30 MODELS • T900 • T1500 Page 1 CEILING / WALL-MOUNT VENTILATORS • 120V READ AND SAVE THESE INSTRUCTIONS WARNING TABLE OF CONTENTS TO REDUCE THE RISK OF FIRE, ELECTRIC SHOCK, OR IN- This manual is divided into sections as follows: JURY TO PERSONS, OBSERVE THE FOLLOWING: •...
  • Page 31 MODELS • T900 • T1500 Page 2 TYPICAL INSTALLATION TYPICAL INSTALLATION MOUNTING (New Frame Construction) WIRING 12” ROUND DUCT BLACK 8” X 12” TO 12” ROUND BLACK EDGE TRANSITION OF HOUSING CEILING GROUND TO JOIST WIRING PLATE (24” centers shown) WIRING PLATE WHITE...
  • Page 32 MODELS • T900 • T1500 Page 3 MOUNTING OPTIONS DUCTING OPTIONS BLOWER DISCHARGE POSITIONS ¼-20 hex nuts secure mounting brackets to housing. Loosen and re-tighten or remove and replace nuts as necessary for desired mounting bracket position. DUCT MOVABLE CONNECTOR PANEL (this side) (Change to this...
  • Page 33 MODELS • T900 • T1500 Page 4 SERVICE PARTS SERVICE PARTS KEY NO. PART NO. DESCRIPTION 97014853 Damper Flap 99150415 Screw, #8B x ¼* (10 req.) 98009520 Duct Connector 97014784 Housing Assembly 97014728 Mounting Bracket (2 req.) 99150591 Mounting Screw (4 req.) 97006142 Wiring Harness 99150471...

This manual is also suitable for:

T050ex

Table of Contents