1. Overview
This controller can be used for solar water heater control and drying oven control.
It has two sensor inputs. The temperature difference between the two sensors
(DT) is used for output control. The controller has two independent outputs also.
One of the output is to controller a cooling device so that DT is limited to a
specified range. The other output is for a heating device so that DT is maintained
to be not less than a specified range.
This controller is a plug and play controller. No wiring is needed for the heater or
cooler. Both the heating and cooling control modes are simple on/off control,
similar to a mechanical thermostat but with much higher precision due to
adjustable hysteresis band, precise sensor and digital read out. Anti-short
function is provided for cooling to protect the compressor from being turned on
with high pressure Freon.
Different operation temperature ranges of the two outputs can be set separately.
Once the cooling range is set, the controller program will automatically limit the
heating range to prevent both heating and cooling from being turned on at the
same time.
Two digital silicon band gap sensors are used. The advantage is being much
more reliable in moisture environment than thermistor sensor. They can be
immersed over extended period of time. They also have a more uniform
accuracy over an entire specified temperature range.
2. Specifications
Temperature Control Range
Temperature Resolution
Temperature Accuracy
Temperature Control Mode
Temperature Control Output
Audio Alarm
Sensor Type
Sensor Size
Sensor1 Cable Length
Sensor2 Cable Length
Operating Temperature
Power Cable Length
Dimension
Input Power
Warranty
* Either the heating or the cooling device is limited to 10 Amps. The output
voltage is the same as the input voltage. When the controller is plugged into
120V AC, the output will be 120VAC. If the controller is connected to 240 VAC,
the output will be 240VAC also.
2017.10
TD220 Differential Temperature Controller
-50 ~ 105° C, -58 ~ 221° F
0.1 ° C (between -9.9 ~ 99 ° C)
1 ° C (between -50 ~ 10 ° C, 100 ~ 170° C)
0.1 ° F (between -9.9 ~ 99.9 ° F )
1 ° F (between -58 ~ 10 ° F, 100 ~ 306 ° F)
0.5 ° C or 0.9 ° F
On/off Control. Heating and Cooling
10A, 120V or 240V AC *
High and Low Limit
Silicon Band Gap Sensor
0.25" O.D. (6.35 mm) x 1" (25 mm) long
6 ft (2 m)
12 ft (4 m)
-20 ~ 50° C (0° F ~ 120° F)
3 ft (1 m)
3.6'' x 5.5'' x 1.8'' (91 x 140 x 46 mm)
85 ~ 240 VAC, 50 Hz / 60 Hz
One (1) year.
Version 1.1 (Oct, 2017)
3. Front Panel
3.1 Descriptions
(a) Display Window. Shows temperature readings and parameters.
(b) Set Key. Press set key to display parameters and save changed values.
(c) Up Key/Mute Alarm. Increase value; mute the alarm buzzer.
(d) Down Key. Decrease value.
(e) Cooling Device Indicator. Synchronized with the power output in the Cooling
Device Socket.
(f) Cooling Device Socket. Supply power to the cooling device. The voltage is
the same as the input power to the controller.
(g) Heating Device Indicator. Synchronized with the power output in the Heating
Device Socket.
(h) Heating Device Socket. Supply power to the heating device. The voltage is
the same as the input power to the controller.
(i) Sensor 1 socket. For the primary sensor which measures the temperature of
the subject to be controlled.
(j) Sensor 2 socket. For the auxiliary sensor which measures the temperature of
the external medium that helps to control the temperature.
4. Setup Flow Chart
During the normal operation, the controller offers three different displaying
modes: temperature reading of Sensor 1, T1; temperature reading of sensor 2,
T2; or, the temperature difference between the two sensors, DT.
Following chart shows how to change the display from one reading to the other.
5.0
78.5
73.5
WWW.AUBERINS.COM
Figure 1. Front panel of TD220.
SET
Temperature reading
Dt
difference between two
SET
sensors(1-2 or 2-1)
SET
Sensor 2
T2
Reading
SET
SET
Sensor 1
T1
Reading
SET
Figure 2. Probe reading Flow Chart
P1/4

Advertisement

loading
Need help?

Need help?

Do you have a question about the TD220 and is the answer not in the manual?

Questions and answers

Summary of Contents for Auber TD220

  • Page 1 Freon. Different operation temperature ranges of the two outputs can be set separately. Figure 1. Front panel of TD220. Once the cooling range is set, the controller program will automatically limit the heating range to prevent both heating and cooling from being turned on at the 3.1 Descriptions...
  • Page 2 AUBER INSTRUMENTS WWW.AUBERINS.COM Press SET key momentarily. the controller will show Dt. Press Down key will Table 1. Parameters Description show T2. Press down key again, the controller will show T1. Press SET when Code Description Setting Range Initial Note Cooling Set Point -58~306 °...
  • Page 3 AUBER INSTRUMENTS WWW.AUBERINS.COM Alarm can be cancelled by press V key. The alarm will not turn on until DT re- enter the alarm zone after it returned to the normal range once. To disable the alarm, set AH = AL.
  • Page 4 Copyright 2007-2017, Auber Instruments All Rights Reserved. No part of this manual shall be copied, reproduced, or transmitted in any way without the prior, written consent of Auber Instruments. Auber Instruments retains the exclusive rights to all information included in this document.