System Settings; Setting System And Fan; Fan Settings - Honeywell T7350 Features

For conventional/heat pump systems
Hide thumbs Also See for T7350:
Table of Contents

Advertisement

Table 1. Default Setpoints.
Control
Occupied
Heating 70°F (21°C) 55°F (13°C)
Cooling 75°F (24°C) 85°F (29°C)

Setting System and Fan

System default setting is Auto. The fan default
is set so the fan operates continuously during:
— Occupied periods,
— Heating and cooling equipment stages in
Not Occupied and recovery periods.
NOTE: Use System and Fan keys to change
settings.
Not Occupied
Standby
67°F (19°C)
78°F (26°C)

System Settings

— Auto: Thermostat automatically changes
between heating and cooling based on
sensed indoor temperature.
— Cool: Thermostat controls cooling.
— Off: Heating, cooling, and fan are all off.
— Heat: Thermostat controls heating.
— Em Heat: Auxiliary heat serves as first stage.
Compressor stages are locked off.

Fan Settings

— On: Fan operates continuously in occupied
and standby periods. Fan cycles with call for
heat or cool during not occupied periods.
— Auto: Fan cycles with call for heating or
cooling during occupied, standby, and
not occupied periods.
NOTE: This is further modified by selection of
conventional or electric heat.
4
63-2604