Programming Temperature Setpoints
1. Press Occupied Heat.
2. Press up
desired temperature is displayed.
3. Press Occupied Cool.
4. Press up
desired temperature is displayed.
5. Press Not Occupied Heat.
6. Press up
desired temperature is displayed.
7. Press Not Occupied Cool.
8. Press up
desired temperature is displayed.
9. Press Run Schedule.
or down
until the
or down
until the
or down
until the
or down
until the
Temperature Setpoint Overrides
IMPORTANT
— Setup determines Occupied override
duration.
— Default duration is three hours.
NOTE: To cancel Override and immediately
return to the program, press Run
Schedule.
T7770 Setpoint Knob
A T7770 setpoint knob can remotely adjust the
T7350 setpoint. This adjustment can be made
when the sensor is in override.
NOTES:
During override, only occupied and
standby heat setpoints, and cool
setpoints are adjusted.
The maximum adjustment is ±5°F.