MAINTENANCE

WARNING: Never attempt
to service heater while it is
connected to propane/LP supply,
operating, or hot. Severe burns
can occur. Any guard or other
protective device removed for
servicing must be replaced prior
to operating the heater.
1. Keep heater clean. Remove any debris
from ventilation openings.
2. Inspect heater before each use. Check
connections for leaks. Apply mixture of
liquid soap and water to connections.
Bubbles forming show a leak that must
be corrected. Correct all leaks at once.
3. Inspect hose/regulator assembly before
each use. If hose is highly worn or cut,
replace it immediately. At least annually,
remove hose/regulator assembly from
heater to inspect entire length of hose.
Replacement hose must be same type
as supplied with unit.
4. Spiders and insects can create a danger-
ous condition that may damage heater or
make it unsafe. Keep burner area clean
of all spiders, webs, or insects.
5. Have heater inspected yearly by a quali-
fied service person.
Ignitor Electrode
White
118994-01J

WIRING dIAGRAM

Electronic
Ignitor
Brown
Gas Light
Burner
White
I
S
Control Module
www.desatech.com

SPECIFICATIONS

• Rating: High - 36,500 Btu/Hr (10.7 kw)
Low - 0,000 Btu/Hr (5.86 kw)
• Fuel: Propane Vapor Only
• Fuel Consumption/Hour: Min. 0.22 gal
(0.8 liter), Max. 0.9 gal (1.48 liter)
Min. 0.9 lb (0.4 kg), Max 1.67 lb (0.76 kg)
• Supply Pressure (To Regulator):
Maximum - 00 psi (1,79 Kpa)
Minimum, for input adjustment - 5 psi
(4.5 Kpa)
• Manifold Pressure: High - 1 psi (6.89 kPa),
Low - 0.98 psi (6.77 kPa)
• Ignitor Gap: 0.120"
• Minimum Temperature: -20°F (29°C)
Surrounding Air Temperature
• Heater Size (L x W x H):
18" x 17.15" x 8" (0.45 x 0.4 x .1 m)
• Carton Size (L x W x H):
8.65" x 18.15" x 18" (0.98 x 0.46 x 0.45 m)
• Heater Weight: 96 lb (4.5 kg)
• Shipping Weight: 110 lb (49.9 kg)
White
Thermocouple
Ground
Brown
Ground
Gas Valve
Black
Control
Orange
Valve
Brown
Brown
Red
Black
ON/OFF
Switch
Battery
Holder