Test Mode ............................7 Pump Control Mode ..........................8 T4000 -T5020 Pump controller ......................10 T4000 Wiring Diagram Setting for Day Tank Control................. 11 T4000 Wiring Diagram Setting for WASTE Tank Control ..............12 T4000-12ALSP ............................. 13 FAQS ..............................14...
Contact Information OLE (UK) Ltd, Barns A & B, Bowely Farm, Bowely Lane, South Mundham, Chichester, West Sussex, United Kingdom PO20 1NB +44 (0)1243 267930 sales@oleuk.com...
Do not touch any connection terminals while energised. Do not attempt to service this item when wet, or in high humidity environment. If the housing of the T4000 becomes damaged, you must shut down and securely isolate this appliance immediately.
PSU Wiring The T4000 has the option of coming with a 240vac to 24vdc PSU as shown below in Figure 1, if a PSU is supplied then 240vac should be wired into the LNE terminals, the output of the PSU is 24vdc and the +- terminals should be wired to the +- terminals of the T4000 as shown in Figure 2.
Product Description The T4000 Alarm / Control unit has 4 digital inputs, this alarm monitor can be operated as a standalone unit, it can also be setup as a Day Tank Pump Controller or sump Controller. Applications Include • Up to 4 x Tank Level Switches: LL, L, H, HH •...
• The BMS volt free output changes when any of the alarms are flashing Red or a solid Red. • The P and A jumper can be set so the T4000 can be used as a Pump controller or as an Alarm.
Alarm Mute • The T4000 has the capability of muting the audible alarm without deactivating The remote output by simply pushing the ALARM/MUTE button, the sounder will be Muted until the button is depressed.
Pump Control Mode The T4000 can easily be configured to make it a pump controller by changing the position of the jumpers as shown in Figure 2. • When control input 2 is triggered, this latches the pump control relay on.
T4000 -T5020 Pump controller You can configure a T5020 with a R5 relay board in conjunction with a T4000 as shown in Figure 3 to provide a visual indication of the tank level in Litres, when used in this mode no float switches are required.
1/ Float switches from OLE are closed (NC), when they are in the DOWN position. 2/ The T4000 inputs can be switched from NC to NO as required using the 2 jumpers on each circuit. 3/ The 0/1 jumper can be removed to disable the Alarm circuit.
1/ Float switches from OLE are closed (NC), when they are in the DOWN position. 2/ The T4000 inputs can be switched from NC to NO as required using the 2 jumpers on each circuit. 3/ The 0/1 jumper can be removed to disable the Alarm circuit.
By a TXX-12VPS-T which is a 12vdc lead acid battery unit which is continuously being charged by a solar panel, power to the T4000 is initiated when the button on the front of the unit is pressed which then keeps the power to the T4000 for a predetermined programmed time.
Q: Can the T4000 be used to control a Tank as well as emptying one. A: Yes, the T4000 can be set to be used either way round and has an emergency automatic shut down when the High level is reached on tank filling applications.