Honeywell T7350 Product Data page 37

Commercial programmable thermostat for single- or mtg512ulti-stage conventional/heat pump systems
Hide thumbs Also See for T7350:
Table of Contents

Advertisement

Configuration Option
Dehumidification Reset Temp
2° F
Setpt
Dehumidification Reheat
None
Dehumidification High Limit
65%
Clock Year
1999
Clock Month
12
Clock Day
Wed
Clock Minutes
11:15 p.m.
Holiday Month
0
Holiday Day
0
Holiday Duration
0 days
Delays
On
System Switch
Auto
Fan Switch
On
Occupied Heat Setpt Stop
55° F
Occupied Cool Setpt Stop
85° F
Not Occupied Heat Setpoint
55° F
Standby Heat Setpoint
67° F
Occupied Heat Setpoint
70° F
Occupied Cool Setpoint
75° F
Standby Cool Setpoint
78° F
Not Occupied Cool Setpoint
85° F
Event 1 State
Occupied
Event 2 State
Not Occupied
Event 3 State
None
Event 4 State
None
Event 1 Time
8:00 a.m.
Event 2 Time
10:00 p.m.
Event 3 Time
12:00 a.m
(midnight)
Event 4 Time
a
The Factory defaults listed here apply to all subbase models with the exceptions of the items listed in Table 21.
b
12:00 Noon is the default start point when time is unknown.
c
Only Available if user selected one or more of following: Dehumidification Reset, Dehumidification Minimum On, or Dehumidification Reheat.
d
Config ID cannot handle Standby setpoints. Keypad users cannot set Occupied setpoints that violate Not Occupied setpoint relationship. The T7350 algo-
rithm never allows the effective setpoint outside Not Occupied setpoints.
Table 20. Thermostat Setup Options Through PDA. (Continued)
PDA
a
Factory Default
Tool CnfgID
X
X
X
X
c
X
X
X
X
X
X
b
X
X
X
X
X
X
X
X
X
X
X
X
X
X
d
X
X
X
X
X
d
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT
Amount of reset used with "Dehumidify Reset". Range: 1 to 5° F.
Must be smaller than occupied zero energy band (ZEB) or standby ZEB.
None: No Reheat dehumidification; Enable: Dehumidification using Reheat.
Dehumidification High Limit. Range: 10 to 90%.
Range: 2000 to 2035.
1: January... 12: December.
Day of the Week: Sun, Mon, Tue, Wed, Thu, Fri, Sat
12:00 a.m.: Midnight (first minute of the day); 12:00 p.m.: Noon.
Unprogrammed; January...December.
Unprogrammed; 1; 2...31; LASTDAYOFMONTH...LAST_SAT
Duration of given Holiday (in days). Range: 0 to 99 days.
On: Delays (on relays, sequential start, etc.) are active.
Off: Delays disabled (also called Test Mode).
System settings: Auto; Cool; Off; Heat; Emergency Heat (valid if Heat Pump)
Fan setting: On; Auto
Occupied Minimum Heat Setpoint: Lowest the programmed occupied heating setpoint
can be adjusted. Range: 40 to 90° F; Value OccHt OccCl - 2° F.
Occupied Maximum Cool Setpoint: Highest the programmed occupied cooling setpoint
can be adjusted. Range: 45 to 99° F. Value OccCl OccHt + 2° F.
Not Occupied heating setpoint. Range: 40 to 90° F.
UnoccHt OccHt OccCl - 2° F; UnoccHt StdByHt StdByCl - 2° F
Standby heating setpoint. Range: 40 to 90° F.
Occupied heating setpoint. Range: 40 to 90° F.
Occupied cooling setpoint. Range: 45 to 99° F.
Standby cooling setpoint. Range: 45 to 99° F.
Not Occupied cooling setpoint. Range: 45 to 99° F.
UnoccCl OccCl OccHt + 2° F; UnoccCl StdByCl StdByHt + 2° F.
Day Schedule is a structure of 8 days of 4 events each day. Defaults listed are for
Monday through Friday. Saturday/Sunday/Holiday default to Unprogrammed (None /
12:00 a.m.). All Events can be set for: Standby or None.
Only Events 1 and 3 can be set for Occupied.
Only Events 2 and 4 can be set for Not Occupied.
Note: The Config ID cannot set an event to Standby, but it can change the time.
Scheduled time for event change.
12:00 p.m.: Noon
12:00 a.m.: Midnight
37
Description
63-2605—5

Advertisement

Table of Contents
loading

This manual is also suitable for:

32006722