Honeywell T7350 Product Data page 36

Commercial programmable thermostat for single- or mtg512ulti-stage conventional/heat pump systems
Hide thumbs Also See for T7350:
Table of Contents

Advertisement

T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT
Configuration Option
Temperature Display
Calibration
TempOverride
RoomTemp
RoomRelHumidity
Discharge AirTemp
Outdoor AirTemp
OccSensor
AuxDO
Key Pad (Lockout)
Recovery Heat RampMin
Recovery Heat RampMax
Recovery Cool RampMin
Recovery Cool RampMax
Recovery Heat OAT@Min
Recovery Heat OAT@Max
Recovery Cool OAT@Min
Recovery Cool OAT@Max
Demand Limit Control Bump
Power Failure Seq Start
Enable DAT High Limit
Enable DAT Low Limit
High Limit DAT Setpoint
Low Limit DAT Setpoint
Dehumidification Min On
Dehumidification Min On Time 5
Dehumidification Reset Temp
a
The Factory defaults listed here apply to all subbase models with the exceptions of the items listed in Table 21.
b
12:00 Noon is the default start point when time is unknown.
c
Only Available if user selected one or more of following: Dehumidification Reset, Dehumidification Minimum On, or Dehumidification Reheat.
d
Config ID cannot handle Standby setpoints. Keypad users cannot set Occupied setpoints that violate Not Occupied setpoint relationship. The T7350 algo-
rithm never allows the effective setpoint outside Not Occupied setpoints.
63-2605—5
Table 20. Thermostat Setup Options Through PDA. (Continued)
PDA
a
Factory Default
Tool CnfgID
No Change
X
3
X
X
Local
X
X
X
X
a
None
X
X
None
X
X
0
X
X
Time of Day
X
X
Enable All
X
X
5° F/hr
X
8° F/hr
X
3° F/hr
X
6° F/hr
X
0° F
X
40° F
X
90° F
X
70° F
X
3° F
X
0 (x10 sec)
X
X
None
X
X
None
X
X
110° F
X
45° F
X
None
X
X
X
None
X
X
No Change: Displayed temperature is actual room temperature.
Can adjust to display up to 3° F (1.7° C) higher or down to 4° F (2.2° C) lower than
room temperature.
Temporary Occupied Override duration. Range: 1 to 8 hours.
Room Temperature Input
Local: Use internal sensor; T7770A/D: Use remote sensor.
T7770B/C: Use remote sensor with setpoint adjustment capability (requires PDA).
T7771: Use remote sensor with setpoint adjustment capability (requires PDA); changes
T7771 LED and bypass button operation: LED on means either occupied or bypass,
pushing bypass can cancel bypass.
Room Relative Humidity Input.
None: No humidity sensor; Local: Use internal humidity sensor;
Remote: Use remote humidity sensor (0-10 Vdc signal).
Discharge Air Temperature Input.
None: No discharge air sensor; or Remote: Remote discharge air sensor.
Outdoor Air Temperature Input.
None: No outdoor air sensor; or Remote: Remote outdoor air sensor.
None: No occupancy sensor; or Remote: Remote occupancy sensor.
Auxiliary Contact Operation:
Time of Day, Economizer, Dehumid Hot Gas BP, or Simple Dehumid.
Auxiliary contact not available if heat pump selected with T7350A.
Keypad lockout enable/disable through special keypad sequence.
Enable All (0): No lockout.
SetPts & Ovrrd (1): Lockout all keys except: Temporary (Not) Occupied,
.
Info Only (2): Lockout all keys except
The special keypress features are never locked out.
Minimum heating recovery ramp rate. Range: 0 to 20° F/hr.
Maximum heating recovery ramp rate. Range: 0 to 20° F/hr.
Minimum cooling recovery ramp rate. Range: 0 to 20° F/hr.
Maximum heating recovery ramp rate. Range: 0 to 20° F/hr.
Minimum heating outdoor air temperature. Range: -20 to 100° F.
Maximum heating outdoor air temperature. Range: -20 to 100° F.
Minimum cooling outdoor air temperature. Range: -20 to 100° F.
Maximum cooling outdoor air temperature. Range: -20 to 100° F.
Demand limit control set point bump. Range: 0 to 10° F.
Delays start of equipment (fan, heat, cool) after power restored to thermostat.
Range: 0 to 150 seconds (in 10-second increments).
None: No Discharge Air Temperature (DAT) high limit; Enable: Use DAT High Limit.
None: No Discharge Air Temperature (DAT) low limit; Enable: Use DAT Low Limit.
Discharge Air Temperature High Limit Setpoint. Range: 65 to 140° F.
Discharge Air Temperature Low Limit Setpoint. Range: 35 to 60° F.
None: No Minimum On Time dehumidification;
Enable: Dehumidification using Minimum On Time.
Minimum on time used with "Dehumidify Minimum On". Range: 5 to 15 minutes.
None: No Reset dehumidification; Enable: Dehumidification using Reset.
36
Description
.
,
and

Advertisement