Page 3
List of changes Revision Date Page Description of Change January, 2017 Major revision “F” compressor changes throughout the manual. August, 2017 54-57 Added IGBT Control Card Replacement instructions. Added R513A refrigerant October, 2017 Updated Figure 95 (SMT Tool Suite Lancher Strip) 123-124 Removed Appendix B Soft Start Board 3 of 132...
Page 4
THIS PAGE INTENTIONALLY LEFT BLANK 4 of 132 M-SV-001-EN Rev.E...
DTC or equipment from other vendors provided that such equipment is intended or revenue, loss of damage or equipment, loss for communication with Danfoss Turbocor of computer programs, loss of data, the costs to equipment over a serial communication link. This substitute these, or any claims by third parties.
Page 12
THIS PAGE INTENTIONALLY LEFT BLANK 12 of 132 M-SV-001-EN Rev.E...
1.1 Purpose This Service Manual is intended to provide service •A functional description of the various procedures specific to the Danfoss Turbocor TT components of the compressor and TG Series compressors. It is not intended to teach basic fundamental safety, refrigeration, •Information regarding procedures necessary...
Example; When 1.3 Commitment to DTC is committed to quality service and customer Danfoss Turbocor is dedicated to satisfying our Quality satisfaction as outlined by our Quality Policy: customers by providing “Best in Class” in terms of quality, value, and on-time delivery while striving for continuous improvement.
“R1234ze(E) with safety classification of A2L. ” ASHRAE Standard 34, 2010 Addendum 1 contains the change to the standard. Compressor Refrigerant Table 1 - Refrigerant Used with Danfoss Turbocor TT Series R134a/R513A Compressors TG Series R1234ze NOTE Do not use recycled refrigerant as it may contain oil, which can affect system reliability. The refrigerant should be pure and stored in virgin containers.
Introduction 5. Wait at least 20 minutes for the DC bus 6. Remove the top cover, taking particular care capacitors to discharge. not to touch ANY components underneath. • • • DANGER • • • Removing the top cover will expose you to a high voltage hazard of up to 860VDC. Wait at least 20 minutes to allow the DC capacitors to discharge and ensure there is no Mains Input voltage present before removing the cover.
Introduction 1. Isolate the compressor power. 2. Clip the ESD strap ground clip to the compressor ground post. See white arrow in Figure 5 (Mains Plate and Ground Post). Figure 5 - Mains Plate and Ground Post Ground Post Mains Plate 3.
Introduction 1.9 DC Bus Test Harness A DC bus test harness must be used when normal operation. When checks are complete, Installation and Removal testing the voltages of the compressor’s power disconnect and remove the test harness. Refer to electronics. The DC bus test harness is not Figure 8 (DC Bus Harness Connection Diagram) designed to be left in the compressor during for a connection diagram.
Introduction 1.9.1 Installation of the 1. Isolate the compressor power and remove the of the Compressor” section of this manual. DC Bus Test Harness top cover as described in the “Electrical Isolation • • • CAUTION • • • Use your ESD wrist strap before touching the Soft Start Board or any electronic components. 2.
Introduction 7. Connect the two plugs of the DC bus test harness into the Soft Start Board. See Figure 11 (Connect Test Harness to Compressor). Figure 11 - Connect Test Harness to Compressor 8. Route the cables through the cable passage on either side of the HV DC-DC Converter, down into the service side.
Introduction 1.9.2 DC Bus Test Harness 1. Install the DC bus test harness as described voltmeter lead into the DC(+F) test harness lead, in the “Installation of the DC Bus Test Harness” and the negative voltmeter lead into the DC(-) section of this manual.
Compressor Fundamentals Compressor operation begins with a demand See the OEM Programming Guide for further signal applied to the compressor. The startup details. sequence is configurable in the startup settings. 2.1 Main Fluid Path The compressor is a two-stage centrifugal type energy is added to the refrigerant.
Compressor Fundamentals Figure 14 - Cooling Inlet Prior to Major Revision “E” Adaptors TT300 Only Major Revision “E” and Later (3/8” with strainer) (1/2” with strainer) All Other Models (1/2” without strainer) Liquid refrigerant is internally channeled to controlled rectifier (SCR) temperature reaches its two solenoid valves.
Compressor Fundamentals Figure 16 - Compressor Motor and Power Electronics Cooling (All Models Except TT300/TG230 Serial Cooling) 25 of 132 M-SV-001-EN Rev.E...
Compressor Fundamentals 2.3 Capacity Control Capacity control of the compressor is achieved impeller rotation to increase energy efficiency primarily by speed modulation. When unloading, during part load operation. the compressor’s first action is to reduce speed to slightly above the minimum (surge) speed for Speed modulation is achieved by the use of the pressure ratio present at the time.
Compressor Fundamentals Figure 17 - Compressor Energy and Signal Flow Connections (TT300/TG230 Shown) The order of power and signal flow through 5. DC bus provides DC voltage to Inverter. the compressor components is as follows (see Figure 17 (Compressor Energy and Signal Flow 6.
Compressor Components This section provides compressor component identification, and steps necessary to replace a locations and functional descriptions, verification component. and troubleshooting methods, cable connection 3.1 Component This section identifies the major parts of the Identification compressor. Figure 19 - Compressor Components Identification (Covers On) Component...
Compressor Components 3.2 Compressor - Removal and Installation • • • CAUTION • • • 3.2 .1 Refrigerant Containment Isolation and recovery of the refrigerant must be performed by a qualified service technician adhering to industry/ASHRAE standards. 1. Close the suction, discharge, and economizer 3.
Page 35
Compressor Components 1.Inspect the compressor to ensure all 4. Remove the motor cooling inlet adapter cap. connections and fasteners are correctly installed. See Section 3.2.3.1 (Compressor Replacement Considerations for Motor Cooling Adapter). 2. Relieve the inert gas pressure through the motor cooling Schrader valve.
Compressor Components Figure 24 - Major Revision “E” Compressor Fittings The following link will provide general http://www.hoseandfittingsetc.com/product/ information on ORFS fittings: fittings/tube-fittings/o-ring-face-seal-fittings/ orfs-nuts-sleeves/ Field installation from old style fitting 3. Source appropriate OEM specified and procured flexible line. Flexible Line 4.
All compressors must be fitted frequency of 50/60Hz. with class T fast-acting fuses to protect the solid state Inverter. Danfoss Turbocor control does Refer to Figure 25 (Main AC Input Terminal) to NOT directly measure 3-phase power values.
Compressor Components 3.3.3 Verification 3.3.3.1 3-Phase AC Input The compressor requires a 3-phase power source Verification with UL-approved or CE-approved components in circuit with code-compliant protection. • • • DANGER • • • This equipment contains hazardous voltages that can cause injury or death. Exercise extreme caution when working on energized circuits.
Compressor Components AC Input Table 9 - Expected AC Voltage Range Nameplate Voltage Acceptable Voltage Range 575VAC 518 to 632VAC 460VAC 414 to 506VAC 400VAC 360 to 440VAC 380VAC 342 to 418VAC 5. If the meter does not show any reading, it 6.
Compressor Components 3.3.4.2 Terminal Block 1. Isolate the compressor power as described 3. Remove the screws that secure the fuse Removal (TT300/TG230) in the “Electrical Isolation of the Compressor” assembly to the SCR at the AC input. Make note section of this manual. of the Soft Start Cable Harness locations.
Compressor Components Figure 32 - Screws Securing Terminal Block to Casting 3. Install the three bus bars to the terminal block 5. Connect the three connectors of the Soft Start and secure them. See Figure 29 (Terminal Block Cable Harness to the bus bars. See Figure 28 Bus Bars).
Compressor Components the DC/DC 7. Using a multimeter set for resistance measurements, place the leads on the ends 6. Using a multimeter set for resistance of the F4 and F5 fast-acting fuses. The reading measurements, place the leads on the ends of should be around 30-38Ω...
Compressor Components 3.5 Silicon-Controlled Rectifier 3.5.1 Function The AC input voltage is connected to the SCRs Board generates the gate signal and outputs by the Mains Input bus bars. The SCRs are used pulses of 0-12VDC to the SCRs to control the in- to convert the AC voltage into DC voltage.
Compressor Components Gate Figure 36 - Silicon-Controlled Rectifier Terminals Gate TT300/TG230 TT350, TT400, TT500, TT700, TG310, TG390, and TT520 5. All other terminals should read infinity or open in both directions (polarity). See Table 10 (SCR Diode Values). Positive (+) Lead Negative (-) Lead Expected Result Table 10 - SCR Diode Values...
Compressor Components NOTE 3.5.3.3 SCR Temperature Sensor Verification The temperature sensor in the SCR manifold is a negative temperature coefficient (NTC) type 10KΩ @ 70°F (21°C). 1. Isolate compressor power and remove the 2. Disconnect the SCR temperature sensor cable Service Side Cover.
Page 47
Compressor Components 3.5.4.3 SCR Installation 1. Apply a thin layer of heat sink paste to the 4. Install the AC Mains Input bus bars. See Figure bottom of the SCRs. 35 (SCR Connections). 2. Install the SCRs to the cooling manifold. 5.
Compressor Components 3.6 DC Bus 3.6.1 Function The DC bus includes the bus bars, DC capacitors, Snubber capacitors reduce noise associated with snubber capacitors, and bleed resistors. See the Inverter switching frequency. Figure 38 (DC Bus Components Identification). Bleed resistors are used to discharge the The SCRs output DC voltage to the bus bars.
Compressor Components 3.6.2 Connections See Figure 39 for location of the DC bus 2. -DC to Soft Start and DC/DC connections. 3. DC bus to Inverter 1. +DC to Soft Start 3.6.3 Verification Use the DC bus test harness to determine if DC bus voltage is within the correct range for the 3.6.3.1 DC Bus Voltage application.
Compressor Components Figure 40 - Removing Attaching Hardware from DC Bus Bars (TT300/TG230 Pictured) 4. Using needle-nose pliers, carefully remove the 7. Remove the snubber capacitors. SCR gate cable harness (TT350, TT400, TT500, and TT700 only). 8. Remove the nylon nuts at the base of the DC Capacitor Assembly, located under the main 5.
Compressor Components 3.6.4.2 DC Bus 1. (TT300/TG230 only) Place the insulating Mylar Installation on the Inverter. See Figure 42 (Insulating Mylar on Inverter). Figure 42 - Insulating Mylar on Inverter (TT300/TG230 Only) 2. Place the DC capacitors and DC bus on the 7.
Compressor Components 3.7 Inverter 3.7.1 Function The function of the Inverter (also known as the DC bus voltage information to the BMCC via the IGBT) is to take the DC bus voltage as an input Backplane. Motor currents and voltages displayed and generate the AC output voltage to the in the SMT cannot be directly compared or compressor motor at the required fundamental...
Compressor Components 3.7.3 Verification This procedure only verifies the Inverter diodes. 3. Remove the DC Capacitor Assembly. The Inverter Control Board cannot be verified in 3.7.3.1 Inverter the field. A faulty Inverter may also appear as an 4. Remove the copper standoffs and fasteners Verification “Inverter Error Signal Active”...
3.7.4 Removal and • • • CAUTION • • • Installation Removal of the Inverter mounting screws will release refrigerant. Isolation and recovery of the refrigerant must be performed by a qualified service technician adhering to industry/ASHRAE standards. This section details the steps to remove and properly and the IGBT Control Card has been install the IGBT Control Card (all models except confirmed to have failed, follow the removal and...
9. Set aside the driver screws for re-use. 10. Properly discard the old driver board. • • • CAUTION • • • Do not move or touch any spring pins unless they are not in proper alignment. Damage or misalignment of spring pins can cause failure of the entire Inverter module.
3. Discard the defective spring pins and inspect the IGBT for any foreign objects. Figure 49 - Spring Pin Removal 4. Insert the new pins carefully and verify they Spring Pins). line up in the notches. Refer to Figure 50 (Seated Figure 50 - Seated Spring Pins 5.
9. Insert the remaining screws and tighten the the first pass and the screws should only be snug screws from center outward according to Figure and not torqued at this step. 52 (Initial Tightening Pass Sequence). This will be Figure 52 - Initial Tightening Pass Sequence 10.
Compressor Components • • • CAUTION • • • Removal of the Inverter mounting screws will release refrigerant. Isolation and recovery of the refrigerant must be performed by a qualified service technician adhering to industry/ASHRAE standards. 3.7.4.3 Inverter Removal 1. Isolate the compressor power as described 9.
Compressor Components 3.8 Motor 3.8.1 Function The motor type employed is a permanent section of the motor is similar in design to a magnet, synchronous speed motor. The winding standard 3-phase star-connected Stator. 3.8.1.1 Stator The Stator operates as the force that drives the shaft, utilizing the HV DC pulses provided to the motor windings by the Inverter.
Compressor Components 3.8.4 Verification • • • CAUTION • • • 3.8.4.1 Stator Insulation Do not attempt to perform an insulation test on a component under vacuum. This can cause insulation breakdown or failure Verification during the testing process. 1. Isolate the compressor power as described 3.
Compressor Components 3.9 High-Voltage DC/DC Converter 3.9.1 Function The HV DC/DC Converter provides the Backplane DC bus voltage (460-900VDC) is supplied to the with +24VDC (with respect to 0V) and HV+ HV DC/DC converter through the Soft Start Board (+250VDC with respect to HV-) for the Bearing F1 fuse.
Compressor Components 3.9.3 Verification 1. Isolate the compressor power as described 3. Turn on the mains power to the compressor. 3.9.3.1 Input Voltage in the “Electrical Isolation of the Compressor” Verification section of this manual. 4. Using the DC bus test harness, verify the expected voltages are present.
Compressor Components 3.9.4 Removal and Installation 3.9.4.1 HV DC/DC 1. Isolate the compressor power as described 4. Loosen the screws next to the Inverter. Converter Removal in the “Electrical Isolation of the Compressor” section of this manual. 5. Remove the screws located on front side of the converter.
Compressor Components 3.10.2 Backplane The Backplane connections and test points are Connections and Test indicated in Figure 60 (Backplane Connections Points and Test Points). Figure 60 - Backplane Connections and Test Points J16: Motor-Cooling Solenoids Control Port +15V Test Point +5V Test Point 24V Test Point J17: SCR Temperature Sensor Port...
Compressor Components NOTE 3.10.2.2 Backplane Verification The test-point LEDs are ON if any voltage is present. The test points must be measured to determine the actual voltage. 1. Remove the Service Side Cover. 5. Using a multimeter set for resistance measurements, place the multimeter leads in 2.
Compressor Components 8. Remove the Backplane from the housing. 3.10.3.2 Backplane 1. Align the Backplane with the mounting Installation 5. Remove the Inverter ground screw from top holes, ensuring the cavity temperature sensor connector is available. right of the Backplane. 2.
BMCC to the Serial Driver. The orifice body. For solenoid identification by actuator cable is clipped to J16 on the Backplane. model, reference the Danfoss Turbocor Spare See Figure 60 (Backplane Connections and Test Parts Guide.
Compressor Components Figure 64 - Motor Cooling Solenoid Actuators 3.12.3 Verification • • • CAUTION • • • 3.12.3.1 Resistance Measurement of Cooling When actuator coils are removed from the solenoids, they must be replaced in the same location. Incorrect installation can result in damage to compressor components.
Compressor Components 3.12.3.2 Output Voltage 1. Remove the Service Side Cover. 3. When the solenoids are energized, measure to Solenoids the +24V test point on the Backplane to verify 2. To ensure the Serial Driver is providing power the Serial Driver is providing power to the motor to the solenoids, look for the Cool-L and Cool-H cooling solenoids.
Compressor Components For split cooling models ONLY mark on the outside of the component or by the presence of an “R” affixed to the coil. See Figure •The actuator coil positions are dedicated. 64 (Motor Cooling Solenoid Actuators). •The coils can be disassembled to verify the wire •The left-side coil can be identified by no mark colors for proper reinstallation.
Compressor Components 3.13.3 Verification 3.13.3.1 IGV Stepper 1. Isolate compressor power. 3. Measure the resistance between terminals 1 Motor Verification and 2, and 3 and 4 of the IGV Motor feed through. 2. Disconnect the compressor controller cable The measured value should be between 46Ω and from the suction pressure/temperature sensor 59Ω.
Compressor Components 3.13.4.1 IGV Removal 1. Isolate compressor power. 3. Detach the connector on the IGV Housing. See Figure 69 (Disconnecting the Power to the IGV 2. To disconnect power to the IGV Motor, remove Motor). the clamp securing the connector. See Figure 68 (IGV Motor Feed Through).
Compressor Components • • • CAUTION • • • 3.14.3 Verification When the BMCC is disconnected from the Backplane, it is important that the Inverter remain connected. Either the BMCC or Inverter is required to be connected to the Backplane before applying power to the compressor. 3.14.3.1 BMCC Power 1.
Compressor Components 3. Reinstall the Serial Driver. 6. If a BMCC that is not original to the compressor is installed, a calibration must be completed and 4. Reinstall Service Side Cover. saved to the EEPROM to match the BMCC to the compressor.
Page 76
Compressor Components 3.15.2.1 Compressor J1 – RS-485 communication port • EXV2 – Pin 1 to 4 Interface Module Connection Descriptions J5 – Liquid Level input • Jumper JP2 required at end of Modbus line. J2 – Input/output • LIQ LEV 1 – Pin 4 to 6 – Liquid level sensor driving the electronic expansion valve1 (EXV1).
Compressor Components - Refer to the Application Manual for thermistor - Refer to the OEM Programming Guide for specifications. software implications. • Spare P: External pressure sensor input D1 to D8 – EXV LED indicators: Red: 2 sets of 4 LEDs for EXV 1 &...
Compressor Components 3.15.3.3 Interlock 1. Ensure the compressor interface cable is • If the measured value is not 0VDC, locate and Verification properly attached to the Backplane and to the remove the source of the voltage. CIM and the BMCC is properly attached to the Backplane.
Compressor Components 3.15.4.2 Compressor I/O 1. Install the left foot of the replacement board 2. Reconnect all external connections and wiring Board Installation into the rail and press the right side of the board on the CIM. down until it engages the rail. 3.
Compressor Components 3.16.2 Connections J1 on the Backplane is the PWM connection port. There are different housings for the Turbocor See Figure 75 (Bearing Power Feed Throughs and compressors. The Major Revision “E” and earlier PWM Connection Port). compressors utilize feed throughs with external male pins while the Major Revision “F”...
Compressor Components NOTE 3.16.3 Verification A faulty PWM Amplifier may be the result of a bearing failure and may cause a failure of the DC/DC resulting in a blown F1 fuse on the Soft Start. If a PWM Amplifier is found to be faulty, the bearing actuator coils, DC/DC and F1 Fuse must also be verified. Several verification methods are available for the •...
Compressor Components Figure 77 - Connecting Leads to PWM Connector and HV- Test Point Red (+) Lead to HV- Major Revision “E” and Earlier Major Revision “F” and Later Black (-) Lead to PWM Molex Connector Black (-) Lead to PWM Connector 6.
Compressor Components 3.16.4 Removal and Installation 3.16.4.1 PWM Amplifier 1. Isolate compressor power and wait for the LEDs disconnect the Molex connector for the PWM and Removal on the Backplane to turn off. bearing feed through. 2. Remove the Serial Driver. 5.
Compressor Components 3.17 Magnetic Bearings 3.17.1 Function The compressor shaft and impellers levitate Figure 80 (Radial Magnetic Bearings) and Figure during operation and float on a magnetic 72 (Axial Magnetic Bearing). Centered rotation is cushion created by the magnetic bearings. instantaneously self-corrected and maintained by Permanent magnets do most of the work and the bearing control loop.
Compressor Components 3.17.2 Connections PWM connectors supply power at the bearing power feed throughs. See Figure 82 (Bearing Power Feed Throughs). Figure 82 - Bearing Power Feed Throughs Major Revision “E” and Earlier Major Revision “F” and Later Front Radial Bearing Power Feed Through Rear Radial and Axial Bearing Power Feed Through...
Compressor Components Figure 85 - Front and Rear Rear Front Bearing Feed Throughs with Molex Connectors 3.17.3.2 Bearing 1. Connect to the compressor using the SMT. 3. In the bearing section, verify the bearing Current Verification amperages displayed are within the range 2.
Compressor Components 3.18 Bearing Sensors 3.18.1 Function Bearing sensors feed back real-time shaft orbit information to the bearing control loop. See Figure 74 (Bearing Control Signal Flow). 3.18.2 Connections The Bearing Sensors are connected internally to The bearing sensor feed throughs are connected the Bearing Sensor feed throughs located above to the bearing sensor cables which connect to J9 the front and rear bearing power feed throughs.
Compressor Components 3.18.3 Verification 3.18.3.1 Bearing Sensor 1. Isolate compressor power and wait for the LEDs • NOTE: There are no connections on Pins 1 & 4 and Resistance Verification on the Backplane to turn off. 1 & 9 on the rear bearing sensor feed through. 2.
Compressor Components 3.19.3 Verification 1. Isolate compressor power. • The Cavity Temperature Sensor is a 10KΩ @ 77°F (25°C) NTC thermistor. The resistance value 2. Remove the Service Side Cover, verifying the should correspond to Figure 91 (Temperature vs. LEDs on the Backplane have turned off. Resistance).
Compressor Components 3.19.4 Removal and Installation 3.19.4.1 Cavity 1. Isolate compressor power. 4. Remove the Serial Driver, BMCC, PWM, and the Temperature Removal Backplane. 2. Isolate the compressor and recover the refrigerant according to industry standards. 5. Remove the cavity temperature sensor. See Figure 92 (Cavity Temperature Sensor Removal).
Compressor Components 3.20 Pressure/ Temperature Sensor 3.20.1 Function The suction and discharge pressure/temperature are used to calculate pressure ratios, saturated sensors are used to inform the compressor of temperatures, superheat and the location within the operating pressures and temperatures at the operating envelope where the compressor is the suction and discharge ports.
Compressor Components Figure 94 - Pressure/ Temperature Sensor Pin Locations 3.20.4 Removal and Installation 3.20.4.1 Pressure/ The following procedure applies to both suction 2. Isolate the compressor; recover the refrigerant Temperature Sensor and discharge pressure/temperature sensors. according to industry standards. Removal 1.
Troubleshooting 4.1 Alarm and Fault The first step in troubleshooting is to gather as and compressor starts, as well as the value of Indications many facts as possible. Compressor fault and pertinent parameters at the time of the fault. event logs provide factual historical information These logs should be reviewed in detail to gain that will indicate the exact reason that the information to allow efficient troubleshooting for...
Troubleshooting Compressor Description Table 18 - Compressor Fault Types Inverter Temperature The measured Inverter temperature has exceeded the fault limit. Discharge Temperature The measured discharge temperature has exceeded the fault limit. Suction Pressure The measured suction pressure has exceeded the fault limit. The measured discharge pressure has exceeded the fault limit.
Troubleshooting Compressor Description Table 19 - Motor Fault Types Motor Single Phase Overcurrent Measured peak current value of any single phase to motor (from Inverter) Fault exceeds the fault limit. The measured DC bus voltage has exceeded the Maximum Bus Voltage DC Bus Overvoltage Fault limit.
Troubleshooting 4.2 Troubleshooting With The Service Monitoring Tools (SMT) software Depending on compressor access level, the the Service Monitoring package can be used to view detailed compressor following tools may be available from the SMT Tools Software information for operational status indications and Tool Suite Launcher Strip.
Troubleshooting Table 21- Service Monitoring Tools Icons (Continued) Icon Tool Description View and configure the compressor operation, shutdown configuration, IGV startup, Compressor Configuration communication configuration, surge/choke, and other operational configuration parameters. View, modify and commit site-specific compressor parameter values of a connected Compressor compressor, as well as import and export configurations between portable files.
Troubleshooting Figure 96 - Fault Trigger Methods Fault Reset: A fault that does not require a A fault demanding a power cycle (Lock-Out power cycle to clear (non-critical) can be reset in Fault) is resettable by cycling the mains power the following manner: Interlock must be closed, to the compressor.
Troubleshooting Table 22 - Compressor Faults Compressor Fault Trigger Troubleshooting Description Method Indicates the Inverter cooling is insufficient. If this fault occurs three times within a 30-minute period, a Lock-Out Fault will occur. CAUTION: Repeated occurrences of this alarm can result in Inverter failure. Ensure the liquid motor-cooling line has sufficient liquid supply and is not blocked.
Page 101
Troubleshooting Table 22 - Compressor Faults (Continued) Compressor Fault Trigger Troubleshooting Description Method Review fault log for indication of values out of specified ranges recorded at time of fault. Verify the questionable sensor and related connections for failure. Inverter temperature: The sensor embedded in the Inverter requires a replacement of the Inverter if determined faulty.
Troubleshooting 4.2.2 Motor Faults/System Status Table 23 - Motor Faults Motor Fault Trigger Troubleshooting Description Method One phase of the Inverter to motor is generating high current. Review Fault and Event Log details to determine conditions related to the fault. This fault can be a result of liquid carryover, a loss of shaft magnetic strength, see Back EMF is Low fault, or Inverter failure, see Inverter Error fault.
Troubleshooting Table 23 - Motor Faults (Continued) Motor Fault Trigger Troubleshooting Description Method Suggests the measured 24VDC supply voltage is out of range. Measure the 24VDC test points at the Backplane. Compare the measured voltages to the displayed readings in the Compressor Monitor Tool and Fault and Event 24VDC Under/Over Log details to determine conditions related to the fault.
Troubleshooting 4.3 Bearing Calibration 4.3.1 When to Calibrate the Bearings 4.3.1.1 Calibration When A bearing calibration can be performed at performed, a calibration report should be created Commissioning commissioning for the purpose of comparing and saved for future comparison. There is no current calibration values to factory saved requirement to save the calibration to EEPROM calibration values.
Troubleshooting Figure 97 - Bearing Calibration Tool If the message “Calibration Failed” or “Levitation •Ensure the RS485 at J1 on the I/O board is Failed” appears when attempting to calibrate, it disconnected from external communication; indicates the steps expected by the SMT have if the chiller controller automatically sets the not been completed.
Troubleshooting 4.3.3 After Calibration is The message “Calibration Complete” appears • Save to EEPROM (If the Save to RAM & EEPROM Complete when all SMT calibration steps are complete, radio button is selected on the Connection regardless of the results. There will be three Manager Window) options available after the calibration has completed.
Troubleshooting 4.3.5 Calibration Report 1. Data in Report: The difference between the • Interpretation: Bearing electrical fault or shaft Analysis “Latest Calibration” and “Stored Calibration” is less is obstructed. than 30 percent. • Action: Verify the bearings. • Interpretation: Successful calibration. •...
Troubleshooting Figure 98 - Bearing Calibration Flow Do not save calibration to EEPROM. Create a calibration report. Return compressor to Successful Re- normal operation Calibration. Return Verify the compressor to bearings normal operation Verify the bearing sensors Could the shaft run Does shaft Shaft is Does shaft levitate...
Troubleshooting 4.4 Compressor • Disconnected: no connection exists with a • No compressor found: Any serial ports or Connection Status compressor or remote compressor host connections have been established, but a valid Indications compressor was not able to be detected •...
Page 110
Troubleshooting • If the SCRs pass test, replace the Soft Start then • If all voltages are within +/- 10%, proceed to repeat Step 13. Step 26. • If one or more of the SCRs test faulty, replace all • If either voltage is not within +/- 10%, isolate three of the SCRs then repeat Step 12.
Troubleshooting 4.5.2 Determining the Cause of an Energy Drain 4.5.2.1 Determining if 1. Remove the Service Side Cover. 4. Remove the Serial Driver. Serial Driver is Draining Energy 2. Test the Backplane voltages at the +24V, +15, 5. Re-apply the compressor power +5, and -15 VDC test points.
Troubleshooting • If all voltages are within (+/- 10%) the PWM is • If any of these voltages are not within (+/- 10%) draining energy. another component is draining energy. 4.5.2.4 Determining 1. Remove the Service Side Cover. • If the +24V reading drops below 22VDC at if Inverter is Draining the moment the demand to drive is given, the Energy...
Troubleshooting 4.5.4 Troubleshooting an 1. Verify the interlock, see Section 3.15.3.3. 4. Move the wire to the SPEED-(neg) at the J2 Open Interlock connector of the I/O board. 2. Ensure there is 0VDC (no external power applied) on the interlock circuit. 5.
Maintenance 5.1 Preventive Table 25 (Preventative Maintenance Tasks) lists Maintenance Tasks tasks that should be performed on a regular basis to maintain optimal performance of the system. Table 25 - Preventive Maintenance Tasks Frequency Item Task 6 Mos 12 Mos Other General Check physical condition of compressor.
Maintenance 5.2 Moisture Prevention Measures 5.2.1 Required Items This section applies to all TT and TG compressors. electrical connections. Condensation issues may become exaggerated in hot and humid The following steps are recommended to prevent conditions. condensate infiltration and stagnation in the Consumables: •...
Maintenance 5. Remove the Motor-Cooling Valve Solenoid Coils by removing the screws on each solenoid. • • • CAUTION • • • The solenoid actuators are dedicated on all models except TT300/TG230. Provide a position reference mark before removal. 6. Dry off any condensate around the solenoids. Figure 100 - Motor Cooling Valve Solenoids 7.
Maintenance 17. Apply thin coating of dielectric grease to gaskets. See Figure 102 (Dielectric Grease Under the underside of bearing power feed through Gasket). Figure 102 - Dielectric Grease Under Gasket 18. Install the greased neoprene gaskets over the through pins. feed through pins.
Maintenance 5.2.1.2 Service Side 1. Install the bearing sensor cables. the exterior of the bearing sensor feed through Assembly connectors. 2. Apply a thin coating of dielectric grease to • • • CAUTION • • • Do not apply any dielectric grease directly to bearing sensor feed through DB9 pins, only apply grease around bearing sensor feed through connectors after the cables are connected to prevent moisture from entering the pin area.
Maintenance Figure 106 - Motor Bus Bar Screws 9. Dry off any condensate around the SCR screws. 13. Wait for surfaces to dry completely. 10. Remove any debris or dust from the SCR 14. Once they are dry, apply a coat of rust screws.
Page 120
THIS PAGE INTENTIONALLY LEFT BLANK 120 of 132 M-SV-001-EN Rev.E...
Part of a centrifugal compressor in the fluid module that transforms the high-velocity, low-pressure gas exiting the impeller into Diffuser high-pressure, low-velocity gas discharged into the condenser. Down-Trip Voltage A voltage threshold where, if the incoming AC voltage drops below it, the Soft Start will shut down. Danfoss Turbocor Compressors Inc. 121 of 132 M-SV-001-EN Rev.E...
Page 122
Appendix A Acronyms/Terms Table 26 - Acronyms/Terms (Continued) Acronym / Term Definition Electrical Erasable Programmable Read Only Memory: A type of non-volatile memory used in computers and other electronic EEPROM devices to store small amounts of data that must be saved when power is removed. It has a limited number of times it can be reprogrammed and an unlimited number of reads.
Page 123
Appendix A Acronyms/Terms Table 26 - Acronyms/Terms (Continued) Acronym / Term Definition Permanent Magnet Type of motor that uses permanent magnets to produce torque. Motor Portable Document Format. A format created by Adobe Systems, Inc. that uses Adobe Acrobat software to create documents that can be shared for reading and printing without needing the source document’s creation tool.
Appendix C Compressor Test Sheet Verification Component Test Point Expected Value Measured Value Section Backplane DC Voltage 0V to 24V 22 to 26 VDC 3.10.2.2 0V to +15V 14.75 to 15.25 VDC 3.10.2.2 -14.75 to -15.25 0V to -15V 3.10.2.2 0V to 5V 4.75 to 5.25 VDC 3.10.2.2...
Page 128
Appendix C Compressor Test Sheet Verification Component Test Point Expected Value Measured Value Section Phase 2: - Lead on AC 0.275V – 0.4V 3.7.3 Output to - DC input Phase 2: - Lead on AC Open 3.7.3 Output to + DC input Phase 3: - Lead on AC 0.275V –...
Page 129
Appendix C Compressor Test Sheet Verification Component Test Point Expected Value Measured Value Section F4 & F5 30-38Ω 3.4.3.2 Solenoid Actuators 4.8 W 108Ω – 132Ω 3.12.3 9.3 W 56.25Ω – 68.75Ω 3.12.3 Stator Resistance Phase 1:2 > 0.0Ω and < 1Ω 3.8.4.2 Phase 1:3 >...
Page 131
Mobile Application | TurboTool® App DanfossTurboTool® App quick access to compressor troubleshooting 24/7 Access to Danfoss Turbocor® compressor troubleshooting on site Scan here to download the App 131 of 132 M-SV-001-EN Rev.E...