T8501 AND T8511 DELUXE ELECTRONIC THERMOSTATS
Minimum-Off Timing
A minimum-off timer assures that the cooling compressor or
heat pump compressor does not come on again for at least
five minutes after it turns off. The minimum-off timer is
triggered when the compressor goes off and when the system
switch is changed. If he compressor turns off when the
setpoint is changed, then the minimum-off timer is triggered.
The minimum-off timer operates during the first stage of both
heating and cooling on the heat pump thermostat models and
cooling only on the standard application models.
Emergency Heat (select models)
When the system is set for Emergency Heat, the auxiliary or
Emergency heat is stage one and the compressor stages are
locked off. Depending on the model, the fan may be activated
when Emergency Heat is used.

Fan Control

The fan will be on when any of these conditions are present
(it can take up to 20 seconds for the fan to turn on).
Fan On:
This setting means that the fan is energized
continuously.
Fan Auto:
The Auto setting means the fan will run only
with the heating and cooling system.
Select models allow the installer the option of electric or
conventional heat fan operation in the installer setup. When
set for electric heat systems, the fan comes on at the same
time as the heat and is energized by the thermostat. The fan
is energized by the plenum switch when set for conventional
heating system.
Outdoor Temperature Sensor (select models)
The outdoor temperature sensor is used to display the
outdoor temperature. Pressing the Information i key once
will show the outdoor temperature if Installer Setup number
24 is set to 02.
WIRING DIAGRAMS (Fig. 13-17)
THERMOSTAT
O
O
G
C
T
T
2
OUTDOOR
TEMPERATURE
SENSOR
FAN
RELAY
1
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND
OVERLOAD PROTECTION AS REQUIRED.
2
AVAILABLE ON SELECT MODELS.
Fig. 13. Typical hookup in heat only standard application.
68-0162—1
W
R
HEATING
RELAY OR
VALVE COIL
1
L1
(HOT)
L2
M15089
O
O
C
T
T
2
OUTDOOR
TEMPERATURE
SENSOR
COOL
CHANGEOVER
VALVE OR
DAMPER
HEAT
CHANGEOVER
VALVE OR
DAMPER
1
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND
OVERLOAD PROTECTION AS REQUIRED.
2
AVAILABLE ON SELECT MODELS.
Fig. 14. Typical hookup in one transformer heat and cool
standard application.
THERMOSTAT
O
O
B
O
T
T
2
OUTDOOR
TEMPERATURE
SENSOR
COMPRESSOR
CONTACTOR
FAN
RELAY
COOL
CHANGEOVER
VALVE
HEAT
CHANGEOVER
VALVE
1
POWER SUPPLY. PROVIDE DISCONNECT MEANS AND
OVERLOAD PROTECTION AS REQUIRED.
2
AVAILABLE ON SELECT MODELS.
Fig. 15. Typical hookup in heat pump application.
12
THERMOSTAT
B
O
G
Y
W
HEATING
RELAY OR
VALVE COIL
COMPRESSOR
CONTACTOR
FAN
1
RELAY
L1
(HOT)
L2
M4821
G
Y
C
L
R
EQUIPMENT
MONITOR
1
L1
(HOT)
L2
R
W1
M15091

Hide quick links:

Advertisement

Table of Contents
loading

This manual is also suitable for:

T8511

Table of Contents