Honeywell T7350 System Engineering page 40

Commercial programmable thermostat
Hide thumbs Also See for T7350:
Table of Contents

Advertisement

T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT
Nv Name
L
ON
nvoBypass
Bypass Out
nvoData1
nvoData1
nvoData2
nvoData2
nvoDischAirTemp
Discharge Temperature
Out
nvoEffectOccup
Effective Occ Out
nvoEffectSetpt
Effective Stpt Out
nvoError
nvoError
nvoFileStat
File Status Out
nvoHeatCool
Application Mode out
63-4368
Table 21. T7350H Network Variable Summary. (Continued)
S
™ Ref Name
Class
PEC
OUT
OUT
OUT
OUT
OUT
OUT
OUT
OUT
OUT
The T7350H uses nvoBypass to command bypass to other XL10
nodes. When the T7350 is in bypass, it commands nvoBypass.
This is a one to many bound relationship. "Many" means one
T7350H can command bypass on all XL10s connected on the
subnet.
Reports whether this device is in timed bypass of the scheduled
occupancy state. Used by other devices to also bypass the time of
day schedule.
Value
State
Action
0
0
This device is not in bypass
Power up value
1
100
This device is in bypass
Reports Manufacturer Specific Device Data including:
bypassTime, coolStgsOn, DaysLeftKeypadHoliday, dischTemp,
effMode, effOccCurrentState, effSetPt, fan, heatStgsOn, oDTemp,
percentCmd,Cool, percentCmdHeat, spaceHumidity, spaceTemp,
subBaseType, sysMode, terminalLoad.
Reports Manufacturer Specific Device Data including: auxRelay,
DALimit, dehumidActive, ESR, holiday, noAuxHeat1, noAuxHeat2,
occSensor, relayAux, relayCool1, relayCool2, relayCool3,
relayFan, relayHeat1, relayHeat2, relayHeat3, remoteStPtOffset,
schedNextState, scheduledState, scheduledTuncos, stagesActive,
T7350CommWorks, temporarySetPt, totalError.
The current discharge air temperature (Celsius). The sensor is
configured by nciConfig.dischAirSensor. A value of 327.67 means
the sensor is not functioning correctly or is out of range.
327.67: Power up value.
Current effective occupancy state:
0: OC_OCCUPIED (power up value).
1: OC_UNOCCUPIED
2: OC_BYPASS
3: OC_STANDBY
-1: OC_NUL
Effective room temperature control set point (Celsius).
327.67: Power up value.
Device error status. Refer to Appendix C - Network Error
Reporting for details.
File transfer status.
Effective operating mode:
0: HVAC_AUTO
1: HVAC_HEAT (heat or re-heat).
3: HVAC_COOL
6: HVAC_OFF (power up value).
7: HVAC_TEST (manual mode or cover in factory test mode).
8: HVAC_EMERG_HEAT
40