Overcurrent Protection Requirements; Assembling And Installing The Dc Input Power Cables - Fujitsu SPARC Enterprise T5140 Installation Manual

Hide thumbs Also See for SPARC Enterprise T5140:
Table of Contents

Advertisement

Related Information
"Overcurrent Protection Requirements" on page 97

Overcurrent Protection Requirements

Overcurrent protection devices must be provided as part of each equipment rack.
Circuit breakers must be located between the DC power source and the server. Use
one 40 A fast-trip double-pole DC-rated circuit breaker for each power supply
unit.
Note – Overcurrent protection devices must meet applicable national and local
electrical safety codes and be approved for the intended application.
Related Information
"Assembling and Installing the DC Input Power Cables" on page 97
Assembling and Installing the DC Input
Power Cables
The following procedure describes how to assemble the DC input power cables for
the SPARC Enterprise T5240 server.
Assemble one cable for each DC power supply in your server.
Assembling and Installing DC Power Cables for the SPARC Enterprise T5240 Server
97