Parameter
ID
Temperature Scale
tS
Dead Band
db
Heat or Cool
OP
Operating Mode
Unoccupied Cooling
uC
Setpoint
Unoccupied Heating
uH
Setpoint
Minimum Cooling
CO
Off Time
Minimum Heating
HO
Off Time
Minimum Cooling
CL
Setpoint (Low Limit)
Maximum Heating
HL
Setpoint (High Limit)
Energy Savings
ES
Configuration
Display of Room
rt
Temperature
WIRING
Table 6. Leadwire Color Code (if fitted)
Terminal
1
Black (BK)
2
White (WH)
3
Orange (OR)
4
Yellow (YL)
5
Gray (GY)
6
Violet (VI)
7
Red (RD)
8
Blue (BU)
9
Brown (BN)
10
11
Table 5. Thermostat Parameter Options
Description
Allows selection of either °C or °F scale Yes
Setting deadband (Zero Energy Band)
Setting operating mode on single relay,
non-changeover models, to either Heat
or Cool
Program unoccupied cooling setpoint
for energy savings.
Program unoccupied heating setpoint
for energy savings
Setting cooling off-time for short cycle
prevention.
Setting heating off-time for short cycle
prevention.
Sets the minimum allowable cooling
setpoint.
Sets the maximum allowable heating
setpoint.
Activate energy savings mode by a
choice of either contact closure or
contact opening.
Allows installer to restrict temperature
display to set point only. With this
parameter, the unit will only display the
set point temperature. Useful where
setpoint limits (HL and CL) will affect
control performance and Room
Temperature display will disagree with
user setpoint.
Color
Use
L1 (Hot)
L2 (N)
Heat
Cool
Damper
Fan Common
Fan Low
Fan Medium
Fan High
–
Energy Mgt.
System
–
T6570, T8570 SERIES DIGITAL FAN-COIL THERMOSTATS
°C Scale
Default
Values
2
2, 3, 4
0
0: cool
1: heat
25
25 to 30
18
10 to 18
0
0, 3, 4, 5
0
0, 3, 4, 5
10
10 to 30
30
10 to 30
1
1: normally open
0: normally closed
1
1: room temp.
0: setpoint only
Fig. 6. Wiring 2-pipe cool-only thermostat with fan On/Auto
7
°F Scale
Default
–
No
4
3, 4, 5
0
0: cool
1: heat
77
77 to 90
65
50 to 65
0
0, 3, 4, 5
0
0, 3, 4, 5
50
50 to 90
90
50 to 90
1
1: normally open
0: normally closed
1
1: room temp.
0: setpoint only
switch.
Values
–
95C-10897–6