Installation

4.1 Installation for cooling metering

4.2 Installation of qp 150

When installing as a cooling meter it is essential that the black cover on the
measuring tube is pointed to the side or down-wards in order to avoid prob-
lems with condensation. Fit the immersion sleeves so that the temperature
sensor is positioned vertically downwards or horizontally.
Fit the electronic unit separate to the volume measurement tube, e.g. on the
wall. Make a loop downwards in order to prevent condensation running along
the connected lines into the electronic unit.
Fig. 14: Recommended installation position for cooling metering
Note: Use flange bolts with a length of at least 100 mm to install the
flanged body in the pipeline.
As an assembly aid 2 M10 threads are mounted on the flange. The threads al-
low for the use of stainless steel eye bolts, for example, for a lifting device.
Note: The measurement insert in the flanged body should be posi-
tioned on the top. This allows a simple exchange of the measure-
ment insert.
Transducer cover
15/49